Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

MGE 3500 with a AP9631CH NMC Critical alarm: DDF file transfer failure

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • MGE 3500 with a AP9631CH NMC Critical alarm: DDF file transfer failure
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 02:05 PM . Last Modified: ‎2024-04-05 02:44 AM

0 Likes
7
1192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:05 PM . Last Modified: ‎2024-04-05 02:44 AM

MGE 3500 with a AP9631CH NMC Critical alarm: DDF file transfer failure

Hi,

 

Running on DCE 7.4.3 and just added this UPS to DCE.  Got the required port opened to be able to transfer between DCE and the UPS with right config for account on the UPS.  Alarm is still there.  I read that maybe I would have to upgrade the firmware on the UPS so I did that.  It is now at version 6.5.0 which I update through DCE.   I even tried to remove the UPS from DCE and add it again but alarm comes back.  What is next step to get the alarm resolved?

 

Thanks

Toby

 

(CID:128754908)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 02:06 PM . Last Modified: ‎2024-04-05 02:44 AM

0 Likes
3
1193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:06 PM . Last Modified: ‎2024-04-05 02:44 AM

Hi Toby,

 

If you've not done so already, check out k-base FA177004. It looks like you've already addressed these points but I just want to be sure. 

 

Another thing to try, if you're using SCP, try instead using FTP for this transfer. You can always change it back later but we want to get that file transferred.

Another thing I'd like to see you try is to get the DDF file manually. You can't add it to DCE but I want to see if the file is available on that unit. Open an FTP session to the device and run the command -  get ddf.zip  do you actually get a file and are there XML files included?Please note that if you run "ls" to look at the directory structure, you will likely not see the ddf.zip file.

 

Thanks,

Steve

(CID:128754940)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 02:06 PM . Last Modified: ‎2024-04-05 02:44 AM

In response to DCIM_Support
0 Likes
0
1193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:06 PM . Last Modified: ‎2024-04-05 02:44 AM

Hi,

According to the event log on the UPS the file is being transfered:

 02/09/2018 09:44:22 apc SSH/SCP: File transfer complete.
 02/09/2018 09:43:44 apc SSH/SCP: File transfer started.
 02/09/2018 09:43:44 apc SCP CLI user 'apc' logged in from X.X.X.X.

I was able to download the file and look at it and it does have XML file in it.  Right now I cannot use FTP because of firewall but I really think the file is being transferred.  Thanks

 

Toby

 

 

(CID:128755075)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 02:06 PM . Last Modified: ‎2024-04-05 02:44 AM

In response to DCIM_Support
0 Likes
0
1193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:06 PM . Last Modified: ‎2024-04-05 02:44 AM

Hi Toby,

I have seen SSH fail in the past so I will see if I can get in contact with someone that has an MGE 3500 with an AP9631CH and test using SCP. Can you run an SNMPwalk of the device? Can you send over the DDF.zip that you downloaded from it? 

 

Steve.  

(CID:128757881)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 02:06 PM . Last Modified: ‎2024-04-05 02:44 AM

In response to DCIM_Support
0 Likes
0
1193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:06 PM . Last Modified: ‎2024-04-05 02:44 AM

Hi Toby,

 

Just an update. I got access to an MGE3500 with an AP9631CH running 6.4.6 firmnware. I turned off FTP. I enabled SSH. I created a device file transfer settings entry for this device using SCP. I then went through with the install and I have received no errors about the DDF file (or anything else for that matter). If you've still got an issue, you may want to try to delete and re-add the device.


Steve

(CID:128760487)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 02:06 PM . Last Modified: ‎2024-04-05 02:44 AM

0 Likes
1
1193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:06 PM . Last Modified: ‎2024-04-05 02:44 AM

Below are the files you requested.  I tried it as you suggested and it is still alarming for transferring the file.  It is Firmware 6.5.0 running on our AP9631CH.

10.101.250.19.walkddf.zip

(CID:128760497)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 02:06 PM . Last Modified: ‎2024-04-05 02:44 AM

In response to DCIM_Support
0 Likes
0
1193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:06 PM . Last Modified: ‎2024-04-05 02:44 AM

Hi Toby,

I upgraded the NMC in the UPS to 6.5.0. As you can see here, I still do not see the issue:

I removed the device and re-added it and still see no issue.

I have FTP server access off and SCP enabled.

I looked at the SNMPwalk you provided and after upgrading my device, I downloaded the DDF.zip file from it so I could make sure they match up as that's how we verify what is downloaded matches what the card believes we should have. 

It does match so the DDF.zip and all it's files are the proper ones for this unit.

All I can suggest is trying to delete the device and re-add it. If the error keeps coming back, there would appear to be something blocking the actual download of the file.

(CID:128760511)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 02:06 PM . Last Modified: ‎2023-10-22 02:59 AM

0 Likes
0
1193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:06 PM . Last Modified: ‎2023-10-22 02:59 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore