Hi,
One of our customer on site received SMS alarm for high return air temperature 6553.3 degree Celsius, the threshold for this was set at 30 degree Celsius. Upon checking the DCE and the CRAC unit on site, the return temperature was in the range of 23.3 degree as shown on the DCE last picture.
I have attached the DDF file we used as well as the screenshots of the device sensors of DCE for your reference.
Screenshots of DCE.docx liebert_ds+pex.zip
(CID:111416031)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:00 PM . Last Modified: 2024-04-08 01:46 AM
I after all could download your zip-file with DDF-file inside. Directly I will tell that it is Modbus DDF-file and, if variable value is equal 65535, then it means the absent or faulty sensor. Moreover, it concerns also other sensors, which are provided at you screenshot, for example, of 65535 run-h. Therefore, most likely is not a bug or an error: just if really your CRAC unit doesn't have these sensors, then these sensors need to be hidden in the DDF-file.
(CID:111939241)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 12:59 PM . Last Modified: 2024-04-08 01:46 AM
Hi Yeoh Chee Leong,
If this problem is appears always, then most likely the mistake in the DDF-file made by the developer. I, for example, found it frequent, including for Liebert conditioners.
P.S.: The DDF-file attached by you is inaccessible for community.
(CID:111416048)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 12:59 PM . Last Modified: 2024-04-08 01:46 AM
I'm sorry for the mistake.. I have emailed the multivendorsupport and they point me here to ask for help with ddf issues.
I've attached the unzipped ddf.
(CID:111937253)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 12:59 PM . Last Modified: 2024-04-08 01:46 AM
Ok, and again [attachment deducted]...
(CID:111937269)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 12:59 PM . Last Modified: 2024-04-08 01:46 AM
I am able to download the file and view it. Let me convert to txt and see if it works.
(CID:111937310)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:00 PM . Last Modified: 2024-04-08 01:46 AM
I after all could download your zip-file with DDF-file inside. Directly I will tell that it is Modbus DDF-file and, if variable value is equal 65535, then it means the absent or faulty sensor. Moreover, it concerns also other sensors, which are provided at you screenshot, for example, of 65535 run-h. Therefore, most likely is not a bug or an error: just if really your CRAC unit doesn't have these sensors, then these sensors need to be hidden in the DDF-file.
(CID:111939241)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:00 PM . Last Modified: 2024-04-08 01:46 AM
Thanks for the assistance, could you direct me on where i can request the customised DDF file without these sensor values? I have spoken to the client and they want them to be removed.
(CID:111937832)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:00 PM . Last Modified: 2024-04-08 01:46 AM
Hi Yeoh Chee Leong,
or, ,
or I have corrected your liebert_ds+pex_MOD.zip and now in DCE nonexistent sensors like run hours won't be displayed.
P.S.: after applied the new DDF-file, the specified sensors, which value are 65535 will "Disconnected". Such sensors should be deleted in DCE, having clicked on them with the right mouse button.
(CID:111939243)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:00 PM . Last Modified: 2024-04-08 01:46 AM
Thanks for the help I'll will arrange to go down and do a check with the user and Emerson personnel to ensure that the sensors are not faulty and update the ddf file.
(CID:111939443)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:00 PM . Last Modified: 2024-04-08 01:46 AM
There is finally corrected liebert_ds+pex_MOD2.zip in which all nonexistent sensors won't be displayed in DCE.
(CID:111939246)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:00 PM . Last Modified: 2023-10-22 02:56 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.