Posted: 2020-07-05 06:38 PM . Last Modified: 2024-04-03 02:55 AM
Hello
We need to keep a metrics data from sensors like PDU and sensor door one years. Would you like clean to me a few point and answer to questions :
1.How much time the sensor’s data is keep ?
2.Where I can change this parameters ?
3.Where I can see this data ?
4.Can I transfer this data via syslog ?
(CID:141270293)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 06:38 PM . Last Modified: 2024-04-03 02:55 AM
Dear Boris,
From your questions:
1.How much time the sensor’s data is keep ?
2.Where I can change this parameters ?
Historical data is stored for as long as the amount of disk space on the DCE appliance allows, but taking into account the purge conditions, which can be viewed and changed in the Storage Settings -> Purge Settings tab (Automatic Purge or Manual Purge).
3.Where I can see this data ?
Similarly, it is possible to look at Storage Settings -> Repositories tab in DCE appliance.
4.Can I transfer this data via syslog ?
Sorry, but this is impossible.
If you have more questions, please ask.
With respect.
(CID:141270312)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 06:38 PM . Last Modified: 2024-04-03 02:55 AM
Many thank for your answer .
Can you clear a addition points :
Is this option available on DCE client or web ?
How I can resize/extend more disk space to DCE ? This is appliance and I can’t access to operation system and I don’t know root password .
(CID:141271381)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 06:38 PM . Last Modified: 2024-04-03 02:55 AM
Dear Boris,
From your questions:
...Is this option available on DCE client or web ?
Everything I said above applies to the DCE-client (not the DCE web-GUI). But the status of the repository can also be viewed in the web-GUI at link http://DCE_IP_or_hostname/nbc/compress/repository/status (you must log in as the DCE-server administrator).
...How I can resize/extend more disk space to DCE ? This is appliance and I can’t access to operation system and I don’t know root password .
This procedure is described in document Adding disk space to a virtual appliance.
Attention: do not increase the size of an existing HDD. This will not help you. It is necessary to add one more separate HDD and restart the DCE-server. This rule applies to both the DCE VM appliance and the DCE hardware appliance.
With respect.
(CID:141271453)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 06:39 PM . Last Modified: 2024-04-03 02:55 AM
Hello
Many thanks again for your answer .
Is there other way for transfer the log to out from DCE ?
Our goal send the log files to Splunk for analysis .
Does possible connect to log files from other system and transfer ?
Sorry about my questions
(CID:141272312)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 06:39 PM . Last Modified: 2024-04-03 02:55 AM
Dear Boris,
DCE appliance - black box by design. Therefore, access to system log-files on a periodic basis is not provided at all.
But for debugging purposes, system log-files can be downloaded from the DCE appliance: how to do this is written in topic .
With respect.
(CID:141272321)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 06:39 PM . Last Modified: 2023-10-22 02:53 AM