Incorrect floor plenum pressure and velocity maps

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Incorrect floor plenum pressure and velocity maps
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:35 AM . Last Modified: ‎2024-04-10 12:50 AM

0 Likes
5
1165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:35 AM . Last Modified: ‎2024-04-10 12:50 AM

Incorrect floor plenum pressure and velocity maps

Hello everone!

I am facing some issues with the air pressure and air velocity maps and I don't know if there is a way to model it properly on DCO.

According to the floor layout of our datacenter, the floor plenum does not expands over the entire surface of the datacenter floor. It is an enclosed area located below each cold aisle and is connected in both sides with the downflow CRACs that supplies cold air to the cold aile.

On top of that, the perforated tiles of the cold ailes of the floor are modular, they can be regulated individually, allowing not to waste cold air in void or semi-used racks.

 

This is the layout of the IT hall and the room where the donwflow CRACs are placed:

This is how CRACs are placed:


In green, the enclosed areas that represents the floor plenum (each of them are isolated from the rest):


When dco generates plenum pressure and velocity maps, it is not taking into account the real configuration of the floor plenum and dropped ceiling of our data center.


This is the floor plenum pressure that calculates DCO, but for my case, I think that the pressure should be calculated only in the enclosed areas (the green rectangles of the image above): 

 

The same issue occurs with the floor plenum velocities, the arrows should only appear in the enclosed areas, or maybe I'm wrong and this is OK:



Does anybody know if there is a way to model it right?

 

Thanks in advance.

(CID:93915141)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:35 AM . Last Modified: ‎2024-04-10 12:50 AM

0 Likes
2
1165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:35 AM . Last Modified: ‎2024-04-10 12:50 AM

Hi Manuel,

The setup you have (at least if the 3 areas a physical separate which I understand they are) is currently not supported in DCO.

A work around would be to model the 3 areas as individual rooms as I see it.

I can however not fully answer if this is correctly understood as you write and has therefore asked for some help from a colleague who will comment once back in the office.

(CID:93915307)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:35 AM . Last Modified: ‎2024-04-10 12:50 AM

0 Likes
0
1165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:35 AM . Last Modified: ‎2024-04-10 12:50 AM

Hi Manuel, we will look into it, thanks for sharing!

(CID:93915243)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:35 AM . Last Modified: ‎2024-04-10 12:50 AM

0 Likes
2
1166
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:35 AM . Last Modified: ‎2024-04-10 12:50 AM

Hi Manuel,

The setup you have (at least if the 3 areas a physical separate which I understand they are) is currently not supported in DCO.

A work around would be to model the 3 areas as individual rooms as I see it.

I can however not fully answer if this is correctly understood as you write and has therefore asked for some help from a colleague who will comment once back in the office.

(CID:93915307)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:35 AM . Last Modified: ‎2024-04-10 12:50 AM

In response to DCIM_Support
0 Likes
0
1165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:35 AM . Last Modified: ‎2024-04-10 12:50 AM

Thanks Søren, unfortunately I cannot model as 3 separate areas because the cold aile containments share the same room. If I try to model as separate rooms, the calculations and physical view that are generated in the 3d view won't be accurate.

(CID:93915310)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:36 AM . Last Modified: ‎2024-04-10 12:50 AM

In response to DCIM_Support
0 Likes
0
1165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:36 AM . Last Modified: ‎2024-04-10 12:50 AM

Hi Manuel, I got some more information from my colleague. Another work around might be to manually set the tile airflow rates to "measured" values. This is a manual process and the values that should be entered could then be calculated by creating the 3 separate rooms/setups as described above and capture the airflow values from these setup(s). Otherwise the values could be entered based on your measurement, design etc. The small disadvantage might be that this would require some manual maintenance if changes happen to the airflow provided by the tiles/system...

(CID:93915399)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:36 AM . Last Modified: ‎2023-10-31 11:08 PM

0 Likes
0
1165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:36 AM . Last Modified: ‎2023-10-31 11:08 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore