Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ITA 9.1.0 - Energy Cost Report

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • ITA 9.1.0 - Energy Cost Report
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
158
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
Gianluca
Gianluca Contributor
Contributor

Posted: ‎2020-08-30 11:32 PM

0 Likes
12
4590
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-30 11:32 PM

ITA 9.1.0 - Energy Cost Report

Hi All

 

last week i have upgrade a Dco to ITA 9.1.0.

backup ad restore was ok.

 

how long customer have to wait to generate Energy Cost Report?

 

thanks a lot

Labels
  • Labels:
  • Data Center Operation
  • DCIM Support
  • IT Advisor
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Jef
Jef Leader
Leader

Posted: ‎2020-09-24 12:19 AM . Last Modified: ‎2020-09-24 12:30 AM

In response to Gianluca
1 Like
0
4322
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-24 12:19 AM . Last Modified: ‎2020-09-24 12:30 AM

Hi Gianluca,

Thanks again for providing data, I could follow and confirm your observations. Here is a short explanation why your energy cost reports (in 9.1) not showing the data as you've expected. In latest release versions including DCO 8.3.x and ITA 9.0.x/9.1 we started to distinguish measured values for whole devices from measured values for device banks. The changes was not applied to Energy Cost report. This resulted in only measurements for banks being visible in report. The problem is that your solution has only measurements for devices, so report has no knowledge of their existence and assumes 0 kWh.
This is resolved in ITA 9.1.1.
I will also contact you by direct email soon.

Kind regards

Jef

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
gsterling
gsterling Mentor
Mentor

Posted: ‎2020-08-31 04:21 AM

0 Likes
11
4577
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-31 04:21 AM

Hello Gianluca.

 

Are you saying your customer does not see the EnergyCost report after the upgrade to ITA?

 

Has the customer tried opening the reports view, and restoring the default designs? This is sometimes necessary.

 

Here is a screenshot of the view I'm referring to from the reports view in the desktop client. Its likely this will cause the energy cost report to appear.

 

RestoreDesigns.JPG

 

Regards

 

Greg Sterling

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Gianluca
Gianluca Contributor
Contributor

Posted: ‎2020-08-31 04:24 AM

In response to gsterling
0 Likes
10
4574
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-31 04:24 AM

Hi Greg

 

not that

 

customer can generate report but without data

 

how long customer have to wait to generate Energy Cost Report?

 

thanks

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

gsterling
gsterling Mentor
Mentor

Posted: ‎2020-08-31 04:29 AM

In response to Gianluca
0 Likes
9
4572
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-31 04:29 AM

What are they seeing in the report output?

 

Do they see their racks but the measurements are showing as 0's?

 

Regards

 

Greg Sterling

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Gianluca
Gianluca Contributor
Contributor

Posted: ‎2020-08-31 04:44 AM

In response to gsterling
0 Likes
8
4568
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-31 04:44 AM

Hi Greg

 

i cannot see any measurements on rack.

 

with Dco v8.2.2 and same license, customer was able to generate it

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

gsterling
gsterling Mentor
Mentor

Posted: ‎2020-08-31 04:56 AM

In response to Gianluca
0 Likes
7
4566
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-31 04:56 AM

Can you send a screenshot or sample report output?

 

There is a bug which was recently found in the newer ITA releases which effects the EnergyCost report and its output. In the case I know about it was causing 0's to be reported where there should have been measurement data for at least some rackpdus. The bug was definitely centered on how measurement data is displayed in the report. This bug is expected to be fixed in 9.1.1 which is due in the near future.

 

What types of devices are in these racks and are their measurements collected from DCE? Can you share sample report output too?

 

Regards

 

Greg Sterling

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Gianluca
Gianluca Contributor
Contributor

Posted: ‎2020-08-31 05:03 AM

In response to gsterling
0 Likes
6
4564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-31 05:03 AM

Hi Greg

 

could i talk to you by Teams?

 

i will show you report

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

gsterling
gsterling Mentor
Mentor

Posted: ‎2020-08-31 05:14 AM

In response to Gianluca
0 Likes
5
4561
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-31 05:14 AM

Yes

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Gianluca
Gianluca Contributor
Contributor

Posted: ‎2020-09-16 08:00 AM

In response to gsterling
0 Likes
4
4387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-16 08:00 AM

Hi

about the issue, customer said that he can see all the info for september but still no data for August

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Jef
Jef Leader
Leader

Posted: ‎2020-09-17 05:52 AM

In response to Gianluca
0 Likes
3
4373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-17 05:52 AM

Hi Gianluca,

 

I will send you an invite to my =S= box shortly, just in case if you would be able to provide the following data:
1- latest backup file from 9.1 setup
2- complete server logs from 9.1 setup
3- screen capture of the issue report (full screen)
4- 8.3.2 backup file, which is used for the upgrade to 9.1
5- server logs from 8.3.2 setup (if that is possible)

then I will see what I can find.

Kind regards,

Jef

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Gianluca
Gianluca Contributor
Contributor

Posted: ‎2020-09-18 05:05 AM

In response to Jef
0 Likes
2
4345
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-18 05:05 AM

Hi Jef

 

im uploading files

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Jef
Jef Leader
Leader

Posted: ‎2020-09-21 03:43 AM

In response to Gianluca
0 Likes
0
4334
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-21 03:43 AM

Thanks Gianluca,

I will look into the data and will get back to you asap,

Kind regards,

Jef

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Jef
Jef Leader
Leader

Posted: ‎2020-09-24 12:19 AM . Last Modified: ‎2020-09-24 12:30 AM

In response to Gianluca
1 Like
0
4323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-24 12:19 AM . Last Modified: ‎2020-09-24 12:30 AM

Hi Gianluca,

Thanks again for providing data, I could follow and confirm your observations. Here is a short explanation why your energy cost reports (in 9.1) not showing the data as you've expected. In latest release versions including DCO 8.3.x and ITA 9.0.x/9.1 we started to distinguish measured values for whole devices from measured values for device banks. The changes was not applied to Energy Cost report. This resulted in only measurements for banks being visible in report. The problem is that your solution has only measurements for devices, so report has no knowledge of their existence and assumes 0 kWh.
This is resolved in ITA 9.1.1.
I will also contact you by direct email soon.

Kind regards

Jef

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore