New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
IT OPTIMIZE SERVER DISCOVERY
EcoStruxure IT Forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-10-0208:10 AM
IT OPTIMIZE SERVER DISCOVERY
Hi Team, we are facing some problems to discovery some servers by SNMP, the server has the SNMP active but when we try to discovery we cant find they, see the pictures attached:
We need to apply some adtional setup to discovery?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-10-0303:24 AM
Hello Fabio. ITO relies on IPMI protocol for discovery of management cards like iDRAC and ILO cards.
SNMP in general cannot be used for server discovery, it is meant for discovery of blade chassis. ITO may be able to discover a server using SNMP if Dell's SNMP agent is installed on the server (not the iDRAC). If the server is using the microsoft SNMP agent it will certainly not work.
In general windows servers should be discovered with WMI, linux servers with SSH, and management cards with IPMI.