Hello everybody
Do you know the procedure of upgrading a DCE v7.2.0 to V7.2.7? I don't find clear information about the procedure required.
I'm interested on migrate the data as well.
Thanks for your help.
(CID:102924868)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 03:37 PM . Last Modified: 2024-04-09 03:05 AM
Angelica,
You can reach out to your local technical support team to receive upgrades for StruxureWare Data Center Expert. Technical support will need to verify software support before providing the upgrades.
http://www.apc.com/site/support/index.cfm/contact-information/
You can upgrade and keep your data for StruxureWare DCE 7.2.0 using the following upgrade path: 7.2.0 > 7.2.1 > 7.2.2 > 7.2.4 > 7.2.5 > 7.2.6 > 7.2.7.
Best Regards,
Cory
(CID:102924871)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 03:37 PM . Last Modified: 2024-04-09 03:05 AM
Angelica,
You can reach out to your local technical support team to receive upgrades for StruxureWare Data Center Expert. Technical support will need to verify software support before providing the upgrades.
http://www.apc.com/site/support/index.cfm/contact-information/
You can upgrade and keep your data for StruxureWare DCE 7.2.0 using the following upgrade path: 7.2.0 > 7.2.1 > 7.2.2 > 7.2.4 > 7.2.5 > 7.2.6 > 7.2.7.
Best Regards,
Cory
(CID:102924871)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 03:37 PM . Last Modified: 2024-04-09 03:05 AM
Thanks Cory, I was needing to understand the required path to upgrade DCE. I'll contact support as well to continue this process. Thanks a lot!
(CID:102924887)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 03:37 PM . Last Modified: 2023-10-31 11:07 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.