How to set 1.5 u size generic path panel in Genome Library in DCO?

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • How to set 1.5 u size generic path panel in Genome Library in DCO?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:49 PM . Last Modified: ‎2024-04-09 01:20 AM

0 Likes
6
1083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:49 PM . Last Modified: ‎2024-04-09 01:20 AM

How to set 1.5 u size generic path panel in Genome Library in DCO?

Hi,

 

I have a problem about DCO device placement.

We used 1.5 u sized patch-panel device. How to resize u of generic patch-panel by modiying generic patch panel model in Genome Library. Is it possible ? Thanks.

the patch panel having 1.5 u sized is Corning WAXWSV-04808-C002


Device attributes is;

http://catalog.corning.com/opcomm/en-GB/catalog/ProductDetails.aspx?pid=21772&vid=8765

(CID:105461548)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:49 PM . Last Modified: ‎2024-04-09 01:19 AM

0 Likes
3
1083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:49 PM . Last Modified: ‎2024-04-09 01:19 AM

On behalf of Eduard: 

Hi Umut,

You can use a workaround.

Change the mounting of your 1.5U patch panel to shelf and give it a height of 66mm (=1.5U).

Use a shelf (from the genomes) or an other device to put it on.

You can remove the shelf ones the patch panel is in place.

Regards,

Eduard

(CID:105461625)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:49 PM . Last Modified: ‎2024-04-09 01:19 AM

0 Likes
0
1083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:49 PM . Last Modified: ‎2024-04-09 01:19 AM

Hi Umut,

Currently in DCO the integer "unit height"/ U values are supported, ie. it is not possible/supported to configure the device U height to be 1.5.

Depending on the setup, I would suggest to configure the device "unit height" to be 1 U or 2 U (depending on how many patch panels you want to add right after each other).

Kind regards

(CID:105461562)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:49 PM . Last Modified: ‎2024-04-09 01:19 AM

0 Likes
3
1084
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:49 PM . Last Modified: ‎2024-04-09 01:19 AM

On behalf of Eduard: 

Hi Umut,

You can use a workaround.

Change the mounting of your 1.5U patch panel to shelf and give it a height of 66mm (=1.5U).

Use a shelf (from the genomes) or an other device to put it on.

You can remove the shelf ones the patch panel is in place.

Regards,

Eduard

(CID:105461625)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:49 PM . Last Modified: ‎2024-04-09 01:19 AM

In response to DCIM_Support
0 Likes
0
1083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:49 PM . Last Modified: ‎2024-04-09 01:19 AM

and if you change the Unit height to 0, it will not add up the U-heights used

(CID:105461735)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:49 PM . Last Modified: ‎2024-04-09 01:19 AM

In response to DCIM_Support
0 Likes
0
1083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:49 PM . Last Modified: ‎2024-04-09 01:19 AM

Thanks for answers, I place 1.5 sized patch panel by using shelf and editing height. But, If I place 2 patch panel 1.5 one after the other , This method is not worked because shelf is not placed in half u? Can Stine Verdelin Hansen help me with about this method ? Thanks; Thanks ;

Ekran Alıntısı.PNG

(CID:105461823)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:49 PM . Last Modified: ‎2024-04-09 01:19 AM

In response to DCIM_Support
0 Likes
0
1083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:49 PM . Last Modified: ‎2024-04-09 01:19 AM

Hi umut.pilge, it was Everard Eduard who provided the workaround. Perhaps he can help? Otherwise you could try Jef's approach below and set the unit height to 2 on one panel and 1 on the next which will give a total of 3 U-heights used. Best, Stine

(CID:105461851)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:50 PM . Last Modified: ‎2023-10-31 11:07 PM

0 Likes
0
1083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:50 PM . Last Modified: ‎2023-10-31 11:07 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore