Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How to push DCE alarms into ServiceNow

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • How to push DCE alarms into ServiceNow
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 06:20 PM . Last Modified: ‎2024-04-03 03:02 AM

0 Likes
4
1761
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:20 PM . Last Modified: ‎2024-04-03 03:02 AM

How to push DCE alarms into ServiceNow

I am looking for more information on how to get alarms from DCE into ServiceNow. I came across this article but it only provides a link to the DCE documentation: 

I understand we can use WebServices to to get the alarms out of DCE, but I need help understanding how this would be configured. Would we use the SDK for this?  Any input would be appreciated. 

Thanks,

 

(CID:141266804)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 06:20 PM . Last Modified: ‎2024-04-03 03:02 AM

0 Likes
2
1760
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:20 PM . Last Modified: ‎2024-04-03 03:02 AM

Hi Justen.  

Do you have a test / dev system with a standalone DCE & SN?  If you do not then proceed in production with extreme caution.  I've seen many attempts like these fail because the receiving system gets flood with alerts, people get emails / SMSs / or tickets to their queue and their understandable upset kills a project that had the potential to provide business benefits

Please also post a little about the business problem you're trying to solve and especially about timing and reliability requirements.  Do you want to see every DCE event in SN?  Do you want the re-arm event, e.g. "the temp is now below upper threshold"?  What can your ServiceNow ingest, receive and pull?   What do the SN people want?  What do your SN users expect and how will you communicate to them about the change to what they see?

Some ideas...

  1. If ServiceNow will ingest traps/informs?, the easiest way at the DCE end is to turn on Network Management System integration.  So I'd look there first.  High risk though as you don't have very fine grained control over what gets sent.  Good choke point as it's easy to turn entire flow on and off.

  2. Another option is to setup Alarm Actions in DCE for individual event types.  Much more work (for you?)  at the DCE end but less risk as per my note above.  You can slowly roll out the system event type by event type.  Sadly this option has no way to shut off the flow completely AFAIK.  If that's important to you then you might consider an intermediate trap receiver / forwarder, a single point of failure granted but a good way to stop the flow entirely if needed

  3. Another option is to have SN "pull" the alarms from the DCE API.  The DCE admin will have little control over this option.

There are probably other options as well and other considerations.  I hope that helps

Kind regards

Ed

 

(CID:141266858)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 06:20 PM . Last Modified: ‎2024-04-03 03:02 AM

In response to DCIM_Support
0 Likes
0
1760
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:20 PM . Last Modified: ‎2024-04-03 03:02 AM

Ed,

 It sounds like option 2 would be the best route to take. One question, if we went with option 3, is there any way to see when the alarm is cleared via web services?

Thanks,

 

(CID:141271664)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 06:20 PM . Last Modified: ‎2024-04-03 03:02 AM

In response to DCIM_Support
0 Likes
0
1760
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:20 PM . Last Modified: ‎2024-04-03 03:02 AM

I guess so but if you're looking at option 2 I imagine the re-arm event will also be sent.

Cheers

Ed

(CID:141271782)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 06:20 PM . Last Modified: ‎2023-10-22 02:33 AM

0 Likes
0
1760
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:20 PM . Last Modified: ‎2023-10-22 02:33 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore