Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How to Change Active Alarm Status to Resolved

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • How to Change Active Alarm Status to Resolved
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
160
Jef
Jef Leader
114
gsterling
gsterling Mentor
79
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 08:11 PM . Last Modified: ‎2024-04-03 01:18 AM

0 Likes
5
1881
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 08:11 PM . Last Modified: ‎2024-04-03 01:18 AM

How to Change Active Alarm Status to Resolved

Hi Team,

Need support to remove  fake "Active Alarm" from UPS device through DCE system. Please see attach UPS device without any Active Alarm but still there is Active alarms in the history without resolved. Can we change status as "resolve" from "Active"  through any configuration change. Your quick reply is highly appreciated.

  

(CID:145851117)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 08:12 PM . Last Modified: ‎2024-04-03 01:18 AM

0 Likes
0
1883
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 08:12 PM . Last Modified: ‎2024-04-03 01:18 AM

Dear Shaik Mahboob Ali,

From your comments:

...and i have change the ddf with correct one then my device alarm working perfectly but this alarm still exist as " Active and As per UPS device PPM there is no alarms & i have hidden it.

This means, that your changes to the DDF-file were not as correct as you think (there is an error in the DDF-file). To check this, you need to remove your problem device from DCE and discover it again.

Therefore, if there are really no alarms on your device, then you need to find your device on the DDF resource and make the corresponding Request modification. And then you will receive a truly correct DDF-file.

Hope this helps you.

With respect.

(CID:145851205)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 08:12 PM . Last Modified: ‎2024-04-03 01:18 AM

0 Likes
1
1883
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 08:12 PM . Last Modified: ‎2024-04-03 01:18 AM

Dear Shaik Mahboob Ali,

I suspect that this is not fake alarms, but active alarms. Just someone has hidden them (hidden alarms are displayed in italics). To see them, you just need to click on the Show Hidden Alarms button as in my screenshot:

Since these alarms are active, you cannot simply give resolved status for understandable reasons. If the alarms are active, then you have problems on the device, and as long as you do not solve them there, the alarms will not be resolved.

Very thanks for the support.

(CID:145851138)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 08:12 PM . Last Modified: ‎2024-04-03 01:18 AM

In response to DCIM_Support
0 Likes
0
1883
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 08:12 PM . Last Modified: ‎2024-04-03 01:18 AM

Hi Thanks for your quick reply. Your are right but there was a problem with DDF of this device , as this same alarm was continuously triggering and i have change the ddf with correct one then my device alarm working perfectly but this alarm still exist as " Active and As per UPS device PPM there is no alarms & i have hidden it. so is there any way to clear this alarm.

(CID:145851171)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 08:12 PM . Last Modified: ‎2024-04-03 01:18 AM

0 Likes
0
1883
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 08:12 PM . Last Modified: ‎2024-04-03 01:18 AM

Dear Shaik Mahboob Ali,

From your comments:

...and i have change the ddf with correct one then my device alarm working perfectly but this alarm still exist as " Active and As per UPS device PPM there is no alarms & i have hidden it.

This means, that your changes to the DDF-file were not as correct as you think (there is an error in the DDF-file). To check this, you need to remove your problem device from DCE and discover it again.

Therefore, if there are really no alarms on your device, then you need to find your device on the DDF resource and make the corresponding Request modification. And then you will receive a truly correct DDF-file.

Hope this helps you.

With respect.

(CID:145851205)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 08:12 PM . Last Modified: ‎2024-04-03 01:18 AM

0 Likes
0
1885
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 08:12 PM . Last Modified: ‎2024-04-03 01:18 AM

Hi Shaik,

If there is no any active alarm present physically at UPS web page then definitely it is DDF issue, send back to development team and ask them to amend.

 

BR,

Haleem Malik

(CID:145851323)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 08:12 PM . Last Modified: ‎2023-10-22 02:24 AM

0 Likes
0
1885
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 08:12 PM . Last Modified: ‎2023-10-22 02:24 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore