How do I send the "Critial Communications Error" emails to only select users and not all users?

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • How do I send the "Critial Communications Error" emails to only select users and not all users?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:14 PM . Last Modified: ‎2024-04-09 03:17 AM

0 Likes
7
706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:14 PM . Last Modified: ‎2024-04-09 03:17 AM

How do I send the "Critial Communications Error" emails to only select users and not all users?

Is there a way to send these emails to only select users? All our LDAP users are getting a copy of these emails, even non-administrators. I found this thread https://community.se.com/t5/EcoStruxure-IT-forum/bd-p/ecostruxure-it-forum that sort of hints that it is not possible but the last post said to ask here so I am.

Thanks in advance for your help

James

(CID:101027954)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:14 PM . Last Modified: ‎2024-04-09 03:17 AM

0 Likes
1
706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:14 PM . Last Modified: ‎2024-04-09 03:17 AM

I am sure someone more knowledgeable will chime in however I asked the same thing (in the forum you found) and the response back was "It is working the way it was designed." Meaning, you can not change that. 

I think that needs to change. Good Luck!

 

Regards,

J

(CID:101613593)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:14 PM . Last Modified: ‎2024-04-09 03:17 AM

0 Likes
1
707
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:14 PM . Last Modified: ‎2024-04-09 03:17 AM

I am sure someone more knowledgeable will chime in however I asked the same thing (in the forum you found) and the response back was "It is working the way it was designed." Meaning, you can not change that. 

I think that needs to change. Good Luck!

 

Regards,

J

(CID:101613593)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:15 PM . Last Modified: ‎2024-04-09 03:17 AM

In response to DCIM_Support
0 Likes
0
706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:15 PM . Last Modified: ‎2024-04-09 03:17 AM

Thanks John, I figured that was going to be the answer but was ever hopeful. James

(CID:101613636)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:15 PM . Last Modified: ‎2024-04-09 03:17 AM

0 Likes
1
706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:15 PM . Last Modified: ‎2024-04-09 03:17 AM

James, how about creating a separate DCE notification policy just for lost comms alarms?
Set an alert action where it will send to specific people for just 
Remove Communication status from default or existing notification policy

Assign all device lost comm to that policy.

p.s You can also assign delay in the 'lost comm policy', e.g 5 mins etc, if you expect communication to return to normal during that period.

Got this from other expert, hope this helped.

 

(CID:101613647)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:15 PM . Last Modified: ‎2024-04-09 03:17 AM

In response to DCIM_Support
0 Likes
0
706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:15 PM . Last Modified: ‎2024-04-09 03:17 AM

Christopherus, Great thought however the Netbotz do not use the DCE Notification system in that way. It doesn't even show up in "Alarm Configuration". If I am wrong, please let me know. Regards, J

(CID:101613696)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:15 PM . Last Modified: ‎2024-04-09 03:17 AM

0 Likes
1
706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:15 PM . Last Modified: ‎2024-04-09 03:17 AM

Hi John,

 

Any system level event or NetBotz lost comm event goes to all users that are configured with an e-mail in the system. Admins should get most of  the server stuff but if you're referring to a lost comm with a NetBotz device specifically, any user (local, LDAP, or AD) that has an e-mail associated with his login and has access to view the NetBotz device in DCE will get these e-mails. 

 

This is indeed working as designed but there is also a plan to change this design for future releases. It's worked this way since NetBotz Central. This change should be in DCE 8 but I can not say if it may make it in any sooner.

 

Steve

(CID:101613695)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:15 PM . Last Modified: ‎2024-04-09 03:16 AM

In response to DCIM_Support
0 Likes
0
706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:15 PM . Last Modified: ‎2024-04-09 03:16 AM

Thanks for the info Steven, I'll pass the info on to our Engineers.

(CID:101613742)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:15 PM . Last Modified: ‎2023-10-31 11:02 PM

0 Likes
0
706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:15 PM . Last Modified: ‎2023-10-31 11:02 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore