How To Mark A Port As Being Used Without Network Path

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • How To Mark A Port As Being Used Without Network Path
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
128
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:20 PM . Last Modified: ‎2024-04-09 02:30 AM

0 Likes
10
1209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:20 PM . Last Modified: ‎2024-04-09 02:30 AM

How To Mark A Port As Being Used Without Network Path

If I have a 24 port copper patch panel in rack is there anyway to show that one (or any number) port is being used without drawing a network connection to another device?

The only option I can think of so far is to open up the patch panel and edit the count.  However this is only valid if there are no back connections on the panel.

(CID:104173976)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 10
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:20 PM . Last Modified: ‎2024-04-09 02:30 AM

0 Likes
2
1209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:20 PM . Last Modified: ‎2024-04-09 02:30 AM

Hi James,

I've just done several tests, but unfortunately it is not possible/supported to mark a port as being used.

I was wondering perhaps either using the "Description" field (Capture-1)

or using the custom properties, and adding a sort of note saying that a certain port is been used, which can also be shown by the tool tip (Capture-2). (but that will not "reserve" the port(s)).

   

 

Kind regards

 

 

(CID:104174001)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:20 PM . Last Modified: ‎2024-04-09 02:30 AM

In response to DCIM_Support
0 Likes
0
1209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:20 PM . Last Modified: ‎2024-04-09 02:30 AM

Thanks Jef Faridi . I was looking at it from a capacity view point so I think maybe the best way would be to decrease/increase the port count on a panel as a cable is added/removed.

(CID:104174008)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:20 PM . Last Modified: ‎2024-04-09 02:30 AM

In response to DCIM_Support
0 Likes
0
1209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:20 PM . Last Modified: ‎2024-04-09 02:30 AM

Hi James, Many thanks for the clarification. Agreed, your suggestion seems to be the best way, thanks.

(CID:104174010)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:20 PM . Last Modified: ‎2024-04-09 02:30 AM

0 Likes
1
1209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:20 PM . Last Modified: ‎2024-04-09 02:30 AM

Agreed, this functionality does not exist today. I do know there is an enhancement request submitted to add this functionality because I submitted it. Here is a quick work-around, it takes some effort to set up, but works. 

Create a set of Custom Properties for the max number of ports a panel can have, 1-48 or 1-96, etc...  Assign list values "Open" and "Used" to each port custom property field. This eliminates typos and missing data when reporting. Then create a custom properties template and assign the customer property port fields to it. Add a patch panel to a rack, assign the port template to the panel.

Looks like this:

 

 

 

Custom Property table:

 

Test SQL:

select ci.ci_name, ci.ci_row_label, ci.ci_rack_label, ci.ci_u_position, cp.cp_name, cp.cp_value

from custom_property cp, configuration_item ci

where cp_name like '%Port%' and cp_value = 'Used' and cp.ci_id = ci.ci_id;

 

Then you can use the Insight Reporting tool and the ETL Export database to create a report to show counts and capacity info based on the Open \ Used entries.

Hope this helps.

 

(CID:104174065)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:20 PM . Last Modified: ‎2024-04-09 02:30 AM

In response to DCIM_Support
0 Likes
0
1209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:20 PM . Last Modified: ‎2024-04-09 02:30 AM

tony.creech Thanks for the suggestion. I like the fact that you get to keep the starting number of ports on the panel/switch for reporting, which with my suggestion that wouldn't be available expect in a custom property.

(CID:104174594)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:21 PM . Last Modified: ‎2024-04-09 02:30 AM

0 Likes
1
1209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:21 PM . Last Modified: ‎2024-04-09 02:30 AM

Hi James,

Since you have reports running against this set of data I would believe that you need this information reflected in your reports, correct? 😀

In this case, and at this point of time, I can see only one solution: create a fake device called, e.g., "Port reserved"  and connect the ports you want to reserve to this device.

 

-Guillaume

(CID:104174490)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:21 PM . Last Modified: ‎2024-04-09 02:30 AM

In response to DCIM_Support
0 Likes
0
1210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:21 PM . Last Modified: ‎2024-04-09 02:30 AM

Vigneron Guillaume I think to include it in the current reports you are correct as it was reliant on back to back connections. As the intent was not to actually do any network patching in DCO I think a simple modification on the standard Network Summary report could do the trick.

(CID:104174596)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:21 PM . Last Modified: ‎2024-04-09 02:30 AM

0 Likes
1
1210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:21 PM . Last Modified: ‎2024-04-09 02:30 AM

A customer asked a similar question. Does anyone know if there have been any updates to this enhancement request?

(CID:129412543)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:21 PM . Last Modified: ‎2024-04-09 02:29 AM

In response to DCIM_Support
0 Likes
0
1210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:21 PM . Last Modified: ‎2024-04-09 02:29 AM

This would be a great tool.. Will check back daily for any new developments. 

(CID:129412959)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:21 PM . Last Modified: ‎2023-10-31 11:06 PM

0 Likes
0
1210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:21 PM . Last Modified: ‎2023-10-31 11:06 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore