How Modifying ITO Server Access SSL certificate

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • How Modifying ITO Server Access SSL certificate
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:01 AM . Last Modified: ‎2024-04-08 04:19 AM

0 Likes
8
1287
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:01 AM . Last Modified: ‎2024-04-08 04:19 AM

How Modifying ITO Server Access SSL certificate

How to modify the SSL certificate for ITO services?
And the Intel Virtual Gateway certificate
The latest JAVA security policy prevents self signed applet open,
The exceptions cannot use wildcards, means I may need to add a lot of exceptions (about 50 IP)

there some device in ITO discovery Virtual KVM Processor Type is N/A,,why ?

 

 

 

KVM allows you to use the proxy connection,
However, if the case is across the network, or can not be opened,
Will direct access to the target device IP, load JViewer.
Is there a way to get all the communications through proxy access?

 

(CID:108828625)

Labels
  • Labels:
  • Data Center Operation
  • Tags:
  • IT Optimize
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:01 AM . Last Modified: ‎2024-04-08 04:19 AM

0 Likes
0
1286
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:01 AM . Last Modified: ‎2024-04-08 04:19 AM

I think there is a process to assign SSL certificates to the management cards. I'm checking into the process and will get back to you. GregS

(CID:108828704)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:01 AM . Last Modified: ‎2024-04-08 04:19 AM

0 Likes
0
1286
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:01 AM . Last Modified: ‎2024-04-08 04:19 AM

Thank you for your reply. I tried a lot of ways to make applet Java not pop up security tips, but without success. Access to the remote process will load multiple applet, each with a security prompt. 1, ITO, SSL Web, self signed certificate. 2, Intel data center manager, self signed certificates, when installed Keytool Java generation. 3, Intel virtual gateway, self signed certificate. 4, VirtualGatewayConsole, applet Java, Intel signature certificate has expired. 5, BMC management card page, HTTPS, self signed certificate. 6, Java applet JViewer, each chip signature certificate, such as AMI. Because the customer's security requirements, can not access the Internet, and therefore can not query the certificate revocation, this will affect the start speed.

(CID:108829002)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:02 AM . Last Modified: ‎2024-04-08 04:19 AM

0 Likes
0
1286
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:02 AM . Last Modified: ‎2024-04-08 04:19 AM

Hi guanyc, has your issue been solved?

Cheers,

Stine

(CID:110013855)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:02 AM . Last Modified: ‎2024-04-08 04:19 AM

0 Likes
0
1286
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:02 AM . Last Modified: ‎2024-04-08 04:19 AM

no....

(CID:110019468)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:02 AM . Last Modified: ‎2024-04-08 04:19 AM

0 Likes
0
1286
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:02 AM . Last Modified: ‎2024-04-08 04:19 AM

My apologies, I lost track of this issue. I will get back to you.

Greg

(CID:111414577)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:02 AM . Last Modified: ‎2024-04-08 04:19 AM

0 Likes
0
1286
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:02 AM . Last Modified: ‎2024-04-08 04:19 AM

Why types of management cards are you trying to discover? I see in your example it appears the vendor is "inspur", are there other types as well. I'm confirming the procedure with Intel, but it appears on initial discussion the certificates would have to be placed on the management cards.

I should have more info next week.

(CID:111937604)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:02 AM . Last Modified: ‎2024-04-08 04:19 AM

0 Likes
0
1286
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:02 AM . Last Modified: ‎2024-04-08 04:19 AM

Intel confirmed you can load your own certificate on the management cards (i.e. ILO, iDRAC Inspur management card).

However the security popups you see when the java app is launched when the vkvm console is started cannot be avoided, at least not today.

Regards

Greg

(CID:113644290)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:02 AM . Last Modified: ‎2023-10-22 02:17 AM

0 Likes
0
1285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:02 AM . Last Modified: ‎2023-10-22 02:17 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore