Posted: 2023-12-31 09:19 PM
Hi,
We have installed the DCE AP9475 at one of our client site. Now our client requires integration of the Access control and CCTV with DCE.
Here we are using the Hikvision brand for CCTV and ACS. Please share the procedure if it is possible.
Need your swift response.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-01 11:25 PM
Hi, StruxureWare DCE is only compatible with Netbotz appliances AFAIK. Only the cameras pods that can be added to the appliance can be used for Surveillance.
I think a similar question as raised a few years back:
https://community.se.com/t5/EcoStruxure-IT-forum/Hikvision-NVR-support-on-DCE/td-p/212619
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-01 11:25 PM
Hi, StruxureWare DCE is only compatible with Netbotz appliances AFAIK. Only the cameras pods that can be added to the appliance can be used for Surveillance.
I think a similar question as raised a few years back:
https://community.se.com/t5/EcoStruxure-IT-forum/Hikvision-NVR-support-on-DCE/td-p/212619
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-02 04:43 AM
Hi justine,
Kindly advise if Hikvision Access control is compatible with DCE or not?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-08 09:19 PM
Hi, No. As far as I know, access control is also limited to Netbotz appliances only.