Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Generex cs141

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Generex cs141
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 05:05 PM . Last Modified: ‎2024-04-03 04:16 AM

0 Likes
7
5997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:05 PM . Last Modified: ‎2024-04-03 04:16 AM

Generex cs141

Hi

 

I can´t log in to the Generex cs141 SNMP card sitting in ABB UPS´s in Datacenter Expert. I works with the old cs121/131

(CID:140216487)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 05:05 PM . Last Modified: ‎2024-04-03 04:16 AM

0 Likes
5
5997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:05 PM . Last Modified: ‎2024-04-03 04:16 AM

I think the default password to access the card to set it up via a web interface is different on the CS141.

From memory - so might be incorrect - admin / cs141-snmp

You should be able to find a manual for the CS141 online that details this.

You may then need to change the SNMP community name(s) or other details on the CS141 card to suit what is already set up in DCE.

Note that the CS141 is a 'generic' style card used by multiple manufacturers and I think some manufacturers change the password to something else...

(CID:140216515)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 05:05 PM . Last Modified: ‎2024-04-03 04:16 AM

In response to DCIM_Support
0 Likes
0
5997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:05 PM . Last Modified: ‎2024-04-03 04:16 AM

Just remembered I had some interesting times with these units, and that there are some strange things regarding the IP addressing on them.  There is a switch inside that forces a particular IP address (possibly 10.10.10.10) to be used and prevents it from being changed.  The switch has to be in the other position to allow it to be changed.

I also had to upgrade the CS141 firmware for it to work at all.

Again there should be manuals online that detail this.

(CID:140217432)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 05:06 PM . Last Modified: ‎2024-04-03 04:16 AM

In response to DCIM_Support
0 Likes
0
5997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:06 PM . Last Modified: ‎2024-04-03 04:16 AM

Hi Garry

 

Thank you for your quick reply. I know all the log in info, settings and so on. I have configured this SNMP card for the last 9 years 😀

 

The problem seems to be that there is no connection to the cs141 when it´s connected in the private lan. It say something like this when I try to log in from Expert. The strange thing is that the SNMP card gets an IP from Expert but it can´t say it´s a UPS when it shows up in Expert. When I did the same procedure with cs121/131 it work without any problem. Only page I could not see is the graphic over the UPS

 

Brgds

Hamid

 

(CID:140217446)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 05:06 PM . Last Modified: ‎2024-04-03 04:15 AM

In response to DCIM_Support
0 Likes
0
5997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:06 PM . Last Modified: ‎2024-04-03 04:15 AM

Maybe I will come to you to get the SNMP part set up next time 😀, it sounds like you know that part better than me...

 

Usually if the device can be connected to and shows up in DCE but is not recognised as a specific device, then it is a DDF problem.  What type of device does DCE think it is? 

Are you trying to use the same DDF as the CS121? I think the DDF is different for the CS141.   Also the system I worked on had a a Generex BACS battery monitoring system tagged onto the back of it through the CS141 and this needed a new DDF creating from scratch, that could see both the UPS and BACS together.

Hope that helps...

 

 

(CID:140217436)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 05:06 PM . Last Modified: ‎2024-04-03 04:15 AM

In response to DCIM_Support
0 Likes
0
5997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:06 PM . Last Modified: ‎2024-04-03 04:15 AM

DCE only say it´s a SNMP device if I remeber right

 

According to Schneider are the latest DDF already in the DCE so I don´t need it and I was told this does not have anything to do with the DDF files. I think it has to do with DDF because is a brand new card, both hardware and software

 

Could you maybe send me the DDF because there is non here to get, it say under development?

(CID:140217444)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 05:06 PM . Last Modified: ‎2024-04-03 04:15 AM

In response to DCIM_Support
0 Likes
0
5997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:06 PM . Last Modified: ‎2024-04-03 04:15 AM

Go here:-  https://ddf.ecostruxureit.com/ and search for Generex BACS, connected to PowerWAVE 9500DPA

That is the DDF I used,  I suspect this will not work properly for you though as it also includes the BACS SNMP OID's 

(CID:140217440)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 05:06 PM . Last Modified: ‎2023-10-22 02:07 AM

0 Likes
0
5997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:06 PM . Last Modified: ‎2023-10-22 02:07 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.