Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Forward DCE events SNMPV3

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Forward DCE events SNMPV3
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
Anonymous user
Not applicable

Posted: ‎2022-02-23 12:23 AM

1 Like
2
1655
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-23 12:23 AM

Forward DCE events SNMPV3

Hello,

 

We have configured forwarding Events to our monitoring system, using "Alarm Configuration" > "Network Management System Intergration" SNMPV3 and we need to get the EngineID to be able to recognize the trpas of the snmpv3 and use the AuthPriv passwords and user to dencrypt the traps.

\

Without the EngineID we can't catch the traps in the monitoring system, we recorded the packets and there is no EngineID.

 

How we can Get or configure the EngineID to be able to dencrypt the traps?

 

Thank You.

 

Regards,

Timoor Dabbour

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
Shaun
Shaun Leader
Leader

Posted: ‎2022-02-23 05:07 AM . Last Modified: ‎2022-02-23 05:09 AM

1 Like
1
1643
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-23 05:07 AM . Last Modified: ‎2022-02-23 05:09 AM

Hi @Anonymous user,

 

I think it's important to note that this integration uses Informs for snmpv3, not traps.

 

When sending v3 traps, the authoritative engine is the engine sending the trap.  When sending v3 Informs, the authoritative engine is the engine receiving the Inform.

 

How this affects what you're looking for here, is that if we were sending a trap, then we should send it with the DCE's engineID.  But when sending it as an Inform, the DCE needs to discover the receiver's engineID.

 

If your receiver correctly handles Informs, what you should expect to see in the packet packet capture, is:

 

  • DCE -> Receiver: empty get-request, with no auth parameters (engineID, etc)
  • Receiver->DCE: report usmStatsUnknownEngineIDs, but this response has an engineID set
  • DCE -> Receiver: informRequest, using the engineID from the previous report
  • Receiver->DCE: get-response, with the same oids as the informRequest sent - this just acknowledges receipt.

 

I've attached a sample of this; the IP ending 78 is a DCE sending a test from the "Network Management System Integration" dialog, and the IP ending 51 is snmptrapd acting as the receiver.  If you want to decrypt the encryptedPDU fields, the paramaters are sha1:secretpassword & aes:secretpassword.

 

 

Attachments
inform.zip
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2022-02-26 11:33 PM

In response to Shaun
0 Likes
0
1626
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-26 11:33 PM

Hello @Shaun ,

 

Appreciate Your Response

 

We will check if the monitoring system can handle this snmp infroms.

 

We wanted to use "Alarm Action" from Device Alarm Configurations tab in addition to the other way to send events

How we can get the Engine ID in that case ?

And if we need another MIBS and not only the Powernet MIBS ?

 

Thank You.

 

Best Regards,

Timoor Dabbour

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore