I have apc 8865's that are daisy chained in pairs. How am I able to update the firmware on the second one? Also I noticed that using the mass config does not seem to work for the second in the chain as well. Is this a bug or am I missing a step?
(CID:89555392)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 08:23 AM . Last Modified: 2024-04-10 01:31 AM
Hello Dave,
We have a knowledge base that explains all options when it comes to Network Port Share. Please navigate to the URL below and search FA164436.
http://www.apc.com/site/support/index.cfm/faq/
(CID:89555402)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 08:23 AM . Last Modified: 2024-04-10 01:31 AM
Ok, Found it thanks. I am a little disappointed that one of the check points during the remote firmware update didn't check for this and fail-out with an error. thanks for the info. dave
(CID:89555403)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 08:23 AM . Last Modified: 2023-10-31 10:59 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.