Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Extending DCO Disk

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Extending DCO Disk
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
160
Jef
Jef Leader
114
gsterling
gsterling Mentor
79
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:46 AM . Last Modified: ‎2024-04-02 11:26 PM

0 Likes
12
2924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:46 AM . Last Modified: ‎2024-04-02 11:26 PM

Extending DCO Disk

I have a DCO-VM that has run out of disk space, can I add more disk but how does it extend, or is only disk added?

Your help please.

 

Regards

Caroll

(CID:153552986)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:46 AM . Last Modified: ‎2024-04-02 11:26 PM

0 Likes
7
2924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:46 AM . Last Modified: ‎2024-04-02 11:26 PM

Dear Caroll Silva,

There are two ways to extend the disk space of DCO and EcoStruxute IT Advisor.

The first method is fast and very flexible, but requires excellent knowledge of the internals of the Linux OS (RHEL/CentOS). Therefore, if you are not like this or you do not have your own Linux system administrators in the organisation, then this method is not suitable for you. Personally, I use this method, since for many years I have been an AIX/Linux administrator.

The second method is the official method, which, for example, was described by Jef Faridi in post :

Manually deleting the system/database files should be avoided, you might risk loosing the data. I would basically suggest the following option, that may give you a reliable setup:

1- Save the current backup files (usually located in the folder /data/backup) somewhere safe (such as network drive)

2- Make a clean/fresh installation (at least 100 GB disc space would be recommended, see System requirements)

3- and then restore the latest completed backup file.

(note: due to disk space issue, some of the latest backup file(s) might be incomplete - check the file size, incomplete backups might be smaller in size).

If you have more questions, please ask.

With respect.

(CID:153553040)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:46 AM . Last Modified: ‎2024-04-02 11:26 PM

0 Likes
2
2924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:46 AM . Last Modified: ‎2024-04-02 11:26 PM

If I remember correctly you can either extend the volume or add a new one in vsphere and then reboot the appliance for the appliance to detect it. 

(CID:153553004)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:46 AM . Last Modified: ‎2024-04-02 11:26 PM

In response to DCIM_Support
0 Likes
0
2924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:46 AM . Last Modified: ‎2024-04-02 11:26 PM

That is for DCE.

(CID:153553082)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:46 AM . Last Modified: ‎2024-04-02 11:26 PM

In response to DCIM_Support
0 Likes
0
2924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:46 AM . Last Modified: ‎2024-04-02 11:26 PM

Thanks for clarifying.

(CID:153945163)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:46 AM . Last Modified: ‎2024-04-02 11:26 PM

0 Likes
7
2924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:46 AM . Last Modified: ‎2024-04-02 11:26 PM

Dear Caroll Silva,

There are two ways to extend the disk space of DCO and EcoStruxute IT Advisor.

The first method is fast and very flexible, but requires excellent knowledge of the internals of the Linux OS (RHEL/CentOS). Therefore, if you are not like this or you do not have your own Linux system administrators in the organisation, then this method is not suitable for you. Personally, I use this method, since for many years I have been an AIX/Linux administrator.

The second method is the official method, which, for example, was described by Jef Faridi in post :

Manually deleting the system/database files should be avoided, you might risk loosing the data. I would basically suggest the following option, that may give you a reliable setup:

1- Save the current backup files (usually located in the folder /data/backup) somewhere safe (such as network drive)

2- Make a clean/fresh installation (at least 100 GB disc space would be recommended, see System requirements)

3- and then restore the latest completed backup file.

(note: due to disk space issue, some of the latest backup file(s) might be incomplete - check the file size, incomplete backups might be smaller in size).

If you have more questions, please ask.

With respect.

(CID:153553040)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:47 AM . Last Modified: ‎2024-04-02 11:26 PM

In response to DCIM_Support
0 Likes
0
2924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:47 AM . Last Modified: ‎2024-04-02 11:26 PM

Thank you for your response, regarding this issue we have another question; Initially 200 GB of disk was allocated, the database it accumulates is 10.48 GB and is in use 150 GB, please indicate what the disk is accumulating.

 

thanks

(CID:153553372)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:47 AM . Last Modified: ‎2024-04-02 11:26 PM

In response to DCIM_Support
0 Likes
0
2924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:47 AM . Last Modified: ‎2024-04-02 11:26 PM

Dear Caroll Silva,

To begin with, if you have access to the webmin interface of your DCO-server, please show a screenshot of Disk and Network Filesystems.

With respect.

(CID:153553385)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:47 AM . Last Modified: ‎2024-04-02 11:26 PM

In response to DCIM_Support
0 Likes
0
2924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:47 AM . Last Modified: ‎2024-04-02 11:26 PM

attached as requested

 

(CID:153553905)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:47 AM . Last Modified: ‎2024-04-02 11:26 PM

In response to DCIM_Support
0 Likes
0
2924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:47 AM . Last Modified: ‎2024-04-02 11:26 PM

Please check the contents of the following folder as its a common reason customers see their partition fill up.

/data/backup

If you see a lot of backup files in this folder, make sure you have set backups to be cleaned up on a schedule per this page: https://sxwhelpcenter.ecostruxureit.com/display/UADCO8x/Backing+up+and+restoring+backup

Cleaning up old backups

In Webclient Administration > Backup and Restore > Backup Settings, you can configure cleanup frequency of old backups.

  1. Specify whether to clean up and how often:
    • Disable: Never clean up
    • Days to keep backups: Delete files older than the specified amount of days
    • Click Save Settings.

Also, check for old / large log files in:

/opt/jboss-as/standalone/log

Existence of log files in this folder is normal, rotated versions will have a .gz file extension. The .gz files can be purged if space is needed.

 

Regards

Greg Sterling

(CID:153554010)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:47 AM . Last Modified: ‎2024-04-02 11:26 PM

In response to DCIM_Support
0 Likes
0
2924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:47 AM . Last Modified: ‎2024-04-02 11:26 PM

Dear Caroll Silva,

Greg Sterling is right, judging from your Webmin screenshot you need to first check the directory with backups (their number and size):

and

With respect.

(CID:153554219)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:47 AM . Last Modified: ‎2024-04-02 11:26 PM

In response to DCIM_Support
0 Likes
0
2923
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:47 AM . Last Modified: ‎2024-04-02 11:26 PM

Thanks for your advisory, we have managed to use the first method of expanding the disk successfully.

regards

 

(CID:153944292)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:47 AM . Last Modified: ‎2024-04-02 11:26 PM

In response to DCIM_Support
0 Likes
0
2923
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:47 AM . Last Modified: ‎2024-04-02 11:26 PM

Ok, very thanks for the good feedback 😀.

(CID:153944410)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:47 AM . Last Modified: ‎2023-10-22 02:04 AM

0 Likes
0
2923
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:47 AM . Last Modified: ‎2023-10-22 02:04 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore