New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Error integrating EMCP 4
EcoStruxure IT Forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-09-2903:45 PM. Last Modified: 2022-09-2903:46 PM
Error integrating EMCP 4
Hello! Could you help me? I have integrated an EMCP 4 generator in the DCE, but when the section to see sensors is opened, values appear but when I turn on the equipment the values do not change and for days it stays that way.
The team's library has already been integrated and even so it does not give me the correct values.
Assuming that this is a Modbus device, as it likely is using the Caterpillar Generator (EMCP4) Modbus DDF, I would recommend polling the Modbus registers that feed those values. This is to ensure that the device is providing the updated values out via Modbus and not just via its interface.