Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Enlogic and Riello DDFs

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Enlogic and Riello DDFs
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:27 AM . Last Modified: ‎2024-04-02 11:34 PM

0 Likes
6
3480
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:27 AM . Last Modified: ‎2024-04-02 11:34 PM

Enlogic and Riello DDFs

Hi

 

I am trying to add some non-APC devices into DCE and experiencing difficulties with either devices not being recognised or the status not being read properly.  We run a mixed estate of a variety of manufacturers (90%+ being APC)

 

Enlogic PDUs

EN1101, EN1113

i have tried using the updated APC DDFs available in DCE 7.7.0 and Enlogic DDFs files in the community from other Enlogic DDFs in the hope that whey would be the same or similar.  However this doesn't seem to work.  I have mixed results with devices being recognised and added, but none of the senors appear to be being read.

 

Will i need to raise a request for new DDFs to be added or can an existing template be ammended?

 

Riello UPSs


These are all based on the Netman 204 Network Card.  We are getting very mixed results with the updated Riello default DCE Template.

 

Riello TM3K40 & DMSTK40AA000 MultiSentry UPSs

1) Issues adding devices into DCE via SNMPV3.   By luck they will either be recognised or experience SNMP communication problems.  If our DCE server can't talk to devices I have tried:

-a) Deleting and rediscovering

-b) Changing the SNMP user, password Auth and Password Encryption levels (even going as far as plain text or no passwords)

-c) Rebooting/disabling and re-enabling the SNMP configuration on the UPS

-D) Rebooting DCE Server (sometimes this will fix one or 2 devices....but then i lose other devices ☹️)

2) Devices will recognise they are a UPS 50% of the time.

3) DCE will read and register some alarms, but once they are resolved, DCE will not update to reflect this.  They also cannot read the Device Alarrm Configurations.

 

Riello CSDL5K0B UPSs

Can be read and recognised properly in SNMP but that's as far as it goes.

 

I have tried using the NETMAN 204 MIBS that have already been created, but rather than resolving the above makes every APC UPS i have believe it's a Riello Netman204 which is not what i need.

 

I have all the MIBS and SNMP Walks if i need to raise new DDFs.  Like the Enlogics though, I wasn't sure if this could be resolved by ammending an existing DDF or not.

 

Any help and advice would be appreciated.

 

Many Thanks,

James

(CID:153093389)

Labels
  • Labels:
  • Data Center Expert
  • DDF
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:27 AM . Last Modified: ‎2024-04-02 11:33 PM

0 Likes
2
3480
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:27 AM . Last Modified: ‎2024-04-02 11:33 PM

Dear James Wyman,

Regarding 3rd party UPS and DCE software: see my answer from topic :

Since you are connecting 3rd party UPS to DCE software, first I highly recommend updating your UPS MIB DDF-file.

Next, please tell us which version of DCE software you are using?

And, in addition, please show a screenshot of the SNMP DDF-files installed in DCE software (their names and versions, a complete list).

Regarding Enlogic rPDU: please tell us which version of the firmware on your rPDU and which version of the SNMP DDF-file are used?

With respect.

(CID:153093393)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:28 AM . Last Modified: ‎2024-04-02 11:33 PM

In response to DCIM_Support
0 Likes
0
3480
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:28 AM . Last Modified: ‎2024-04-02 11:33 PM

Hi spezialist

 

Thank you for your reply.

 

  • DCE Version is 7.7.0 - (We will be Upgrading to 7.8.0 in January after our change freeze)
  • Current Active DDF List: See below

 

ENLOGIC

 

  • Enlogic rPDU SNMP DDF is (Version 20)

  • Enlogic rPDU Firmware Revision: 7.12R3G (EN1101) & 7.12RR39 (EN1113)

  • I have tried ENLOGIC PDU from the Community Download DDF list peviously but since removed this.

 

RIELLO


  • After looking at the other thread you referenced The version of 3rd Party UPS MIB is Version 11.
  • I did try the Netman 204 DDF from the community forum but removed this after undesired effects (all our UPSs including APC being renamed and changed to Netman_204)


After some further digging, some of the issues may/may not also be related to the Riello Fimware version we are using on our devices.

  • The Multisentry TM3K40/DMSTK40AA000 are on 2 different versions of firmware (see below).  Both look to have known SNMP communication issues that are fixed in later UPS OS and firmware updates.

 

  • The Riello CSDL5K0B Sentry's are on older firmware still and i imagine will need the same firmware updates performing.

 

The latest version of Netman 204 on Riello's Website is S19-2 03.07.

https://www.riello-ups.co.uk/downloads/25-netman-204

 

Is it worth me upgrading straight to this or to a different version?  As we are looking to update to DCE 7.8.0 in January will this change anything regarding which firmware you currently support in your 3rd Party UPS MIB List?

 

Thanks for your time.

James

(CID:153093412)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:28 AM . Last Modified: ‎2024-04-02 11:33 PM

In response to DCIM_Support
0 Likes
0
3480
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:28 AM . Last Modified: ‎2024-04-02 11:33 PM

Dear James Wyman,

Please look at your e-mail.

(CID:153093651)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:28 AM . Last Modified: ‎2024-04-02 11:33 PM

0 Likes
1
3480
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:28 AM . Last Modified: ‎2024-04-02 11:33 PM

Dear James Wyman,

Regarding the Enlogic rPDU: the specified version of the DDF-file v.20 has not been relevant for a long time. The latest version of the DDF-file is v.23. Please reply to my private e-mail and I will send it to you.

Regarding UPS Riello: DCE software upgrade will not solve your problem, especially with SNMP v3 protocol. You've noticed correctly, it may be necessary to bring the firmware version of all your Riello UPS to the latest version and try SNMPv1 or SNMPv2 first.

With respect.

(CID:153552274)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:28 AM . Last Modified: ‎2024-04-02 11:33 PM

In response to DCIM_Support
0 Likes
0
3480
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:28 AM . Last Modified: ‎2024-04-02 11:33 PM

Dear James Wyman,

In any case, you can contact me with questions regarding the DDF-file for Enlogic devices.

Regarding Riello UPS: if this is critical for you, then you need to refer to the DDF resource in order to create a request for modifying an incorrectly working DDF-file. This will be the right decision.

In addition, I want to draw your attention to Charlotte Arroyo answer in post  regarding the details of ordering DDF-files from =SE=.

With respect.

(CID:153553334)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:28 AM . Last Modified: ‎2023-10-22 02:02 AM

0 Likes
0
3480
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:28 AM . Last Modified: ‎2023-10-22 02:02 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore