New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
EcoStruxure AS-P - Can this device carry more than 1 trunk of field devices with different comm protocols?
EcoStruxure IT Forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-11-0608:08 AM
EcoStruxure AS-P - Can this device carry more than 1 trunk of field devices with different comm protocols?
Hi Community members,
I'm currently looking for a replacement of an old Tridium JACE NXT master controller that crapped out. The existing tridium JACE was carrying a LonWorks trunk with 27 MNL 800 devices and an ASD trunk with 25 MZ|| devices. I believe the solution would be to use an AS-P to replace the Tridium JACE but wanted to confirm if 1 AS-P is sufficient to carry the 2 trunks and support all the field devices?
would I need a separate AS-P for each trunk?
Thank you all in advance, really appreciate any feedback on this.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-11-0708:21 PM
@Sk14 Yes an AS-P can have both LON and ASD networks concurrently. However the ASD protocol is not supported in EBO 2022 and later. You can have an EBO 2022 or 2023 ES, but the AS-P must stay at EBO 3.2.x.