i want to monitor my eaton UPS with DC Expert, what are the requirements for it and how can i get the mib files n get them incorporated in DC Expert.
(CID:94602241)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 11:04 AM . Last Modified: 2024-04-10 12:40 AM
Hi Shaf,
I found some Eaton stuff on: http://powerquality.eaton.in/Support/Software-Drivers/Default.asp
Please confirm if the MIB you are looking for is available there. The next step would be to email this MIB to multivendorsupport@apc.com & they will search through their base if they have the DDFs(Device Definition Files) ready for the UPS or they will create one for you. Once you receive the DDF, you can upload it to DC Expert under Device> SNMP Device Communication Settings & start discovering your UPS.
(CID:94602247)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 11:04 AM . Last Modified: 2023-10-31 10:56 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.