Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Please select a country to continue with beta search.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 07:09 PM . Last Modified: 2024-04-03 02:45 AM
Building Dashboard status for our UPS's, On the Eaton DCE does not seem to collect the value "Percentage Full Load". It is a value available on the UPS management console. How do I acquire for DCE. I have all other Eaton values available.
Thanks,
(CID:143756415)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 07:09 PM . Last Modified: 2024-04-03 02:45 AM
Hi Enrique,
DCE can poll any value available via SNMP. If a device has a value available in the UI, it does not automatically mean that it has that value available via SNMP. I am not familiar with the specific device but to verify what is available from that device, you'll want to look at that device's MIB to see if the vendor has it available. Then you'll want to do an SNMP get or SNMPwalk of the device to see if the specific OID is returned from that device. If it is not returned, it's simply not available. If it is returned, you may want to check with the DDF team to see if the DDF used for this device has the correct SNMP OIDs available. You can communicate to the DDF team through this link:
https://ddf.ecostruxureit.com/
Thanks,
Steve
(CID:143756890)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 07:09 PM . Last Modified: 2023-10-22 01:58 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.