Posted: 2025-03-07 06:22 AM . Last Modified: 2025-03-07 06:22 AM
Hello,
I do not have a setup with this tested, nor do I think it has been directly tested by anyone. From a theoretical standpoint, it should work as the A-Link pinout would be the same for powering the actuators and the relay controls should work on a similar basis with being able to be controlled by a temperature sensor.
Something to keep in mind with the 250 and 750 is that A-Link can only provide so much power, so if there are other items plugged into A-Link as well, you may need to add an external power adapter to a sensor pod or rack access pod in the chain.
Regards,
Cory