ETL internal database

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • ETL internal database
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:23 AM . Last Modified: ‎2024-04-09 12:56 AM

0 Likes
12
2087
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:23 AM . Last Modified: ‎2024-04-09 12:56 AM

ETL internal database

I'm scoping the work required to upload about 100-200 items and values from an external bms into dco using the etl internal database.  I've some questions, hope someone can help me.  Thank you so much.

  1. After creating an ETL internal PostgreSQL database, I need to create items in the empty database.  Is there a configuration tool (with GUI) that I can use to easily add or to remove items to/from the database?  A tool that even an entry level service technician can add new items without knowing how to use ETL.

  2. I want to know if I can update the values of the items that I've created directly on the PostgreSQL internal database?  For example:

    e.g. UPDATE CONFIGURATION_ITEM_MEASUREMENT SET cim_value= "25.0", state_flag = "new" WHERE ci_id = "temp1";

(CID:105466856)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:23 AM . Last Modified: ‎2024-04-09 12:56 AM

0 Likes
7
2086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:23 AM . Last Modified: ‎2024-04-09 12:56 AM

Perhaps pgadmin would help?  It's meant for DBAs but might be OK for entry level service technician with some guidance from you - it's point and shoot, tree style with a few helper features.

http://www.pgadmin.org/download/

Last time I tried I (for my Win 7 64 bit machine) I ended up downloading the entire PSQL software, the actual RDBMS I don't run on my laptop - I just use the pgadmin part to connect to ETL import/export

Good luck

Cheers

 

(CID:105466863)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:23 AM . Last Modified: ‎2024-04-09 12:56 AM

0 Likes
7
2087
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:23 AM . Last Modified: ‎2024-04-09 12:56 AM

Perhaps pgadmin would help?  It's meant for DBAs but might be OK for entry level service technician with some guidance from you - it's point and shoot, tree style with a few helper features.

http://www.pgadmin.org/download/

Last time I tried I (for my Win 7 64 bit machine) I ended up downloading the entire PSQL software, the actual RDBMS I don't run on my laptop - I just use the pgadmin part to connect to ETL import/export

Good luck

Cheers

 

(CID:105466863)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:23 AM . Last Modified: ‎2024-04-09 12:56 AM

In response to DCIM_Support
0 Likes
0
2086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:23 AM . Last Modified: ‎2024-04-09 12:56 AM

Ed, appreciate your reply. Thanks. pgadmin is useful. By the way, any chance that you have a clue on my 2nd question?

(CID:105466868)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:23 AM . Last Modified: ‎2024-04-09 12:56 AM

In response to DCIM_Support
0 Likes
0
2088
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:23 AM . Last Modified: ‎2024-04-09 12:56 AM

You can do such updates. You have to mark the corresponding row 'changed' for Operation to see that the values have been updated.

(CID:105466888)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:23 AM . Last Modified: ‎2024-04-09 12:56 AM

In response to DCIM_Support
0 Likes
0
2086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:23 AM . Last Modified: ‎2024-04-09 12:56 AM

Hi CP, PGAdmin would work as Ed Tarento suggested. You can also try https://www.dbvis.com/download/evaluate/ or any other similar tools. The updates you asked for should work as far as your query is fine. For production, would you develop some sort of scripts that automatically read values from BMS and updates the db? A manual process to update the db as needed works for testing and validation but is not ideal for customer production environment.

(CID:105467035)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:23 AM . Last Modified: ‎2024-04-09 12:56 AM

In response to DCIM_Support
0 Likes
0
2088
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:23 AM . Last Modified: ‎2024-04-09 12:56 AM

Hi Ed, I used pgadmin, I'm able to import item_configuration records but not the related item_configuration_measurement.

(CID:105467943)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:23 AM . Last Modified: ‎2024-04-09 12:56 AM

In response to DCIM_Support
0 Likes
0
2086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:23 AM . Last Modified: ‎2024-04-09 12:56 AM

Ajay Nagar Can you assist ? I have limited time right now

(CID:105467998)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:23 AM . Last Modified: ‎2024-04-09 12:56 AM

In response to DCIM_Support
0 Likes
0
2086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:23 AM . Last Modified: ‎2024-04-09 12:56 AM

For the power measurements, please take a look here (if you haven't already): https://dcimsupport.apc.com/display/DCIMDEVELOPER/ETL+Integration+Examples

(CID:105468012)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:24 AM . Last Modified: ‎2024-04-09 12:56 AM

In response to DCIM_Support
0 Likes
0
2086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:24 AM . Last Modified: ‎2024-04-09 12:56 AM

Hi CP, please provide more details. Do you see any errors? You have to associate the imported configuration_items to DCO devices, save, and run the transformation again to be able to see measurements on power tab. Can you upload screenshot of ci_measurement table in pgAdmin?

(CID:105468052)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:24 AM . Last Modified: ‎2024-04-09 12:56 AM

0 Likes
2
2086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:24 AM . Last Modified: ‎2024-04-09 12:56 AM

Hi CP

I now have a requirement to do the exact same thing as you have requested in this post

Did you get it working?  It would be good to share experience

Cheers

Ed

 

(CID:106891227)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:24 AM . Last Modified: ‎2024-04-09 12:56 AM

In response to DCIM_Support
0 Likes
0
2086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:24 AM . Last Modified: ‎2024-04-09 12:56 AM

Hi Ed, Unfortunately not. My user decided to use Pentaho script. I did the following and it didn't work. OnCreateAction=INSERT INTO configuration_item (ci_id, cit_id, ci_name, state_flag) VALUES ('{opc_item_id}', 0, '{point_description}', 'new') ON CONFLICT DO NOTHING;INSERT INTO configuration_item_measurement (cim_id, ci_id, cim_value, mu_id, mc_id, mt_id, state_flag) VALUES ('{opc_item_id}_measurement', '{opc_item_id}', '{source_value}', 0, 0, 0, 'new') ON CONFLICT DO NOTHING; OnUpdateAction=UPDATE configuration_item SET ci_name = '{point_description}', state_flag = 'changed' WHERE ci_id = '{opc_item_id}'; OnValueChange=UPDATE configuration_item_measurement SET cim_value = '{source_value}', state_flag = 'changed' WHERE ci_id = '{opc_item_id}'; I believe my user did what Ajay Nagar recommended below: You have to associate the imported configuration_items to DCO devices, save, and run the transformation again to be able to see measurements on power tab. If you managed to get it to work, please share. Thank you.

(CID:106891243)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:24 AM . Last Modified: ‎2024-04-09 12:56 AM

In response to DCIM_Support
0 Likes
0
2086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:24 AM . Last Modified: ‎2024-04-09 12:56 AM

You have to set the types of the measurements correctly. The 0, 0, 0 values for mu_id, mc_id and mt_id are not enough. Please check here: ETL Integration Examples, and let me know if you need more inputs.

(CID:106891365)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:24 AM . Last Modified: ‎2023-10-31 10:57 PM

0 Likes
0
2086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:24 AM . Last Modified: ‎2023-10-31 10:57 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore