ETL integration error

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • ETL integration error
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:16 PM . Last Modified: ‎2024-04-08 12:41 AM

0 Likes
12
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:16 PM . Last Modified: ‎2024-04-08 12:41 AM

ETL integration error

Dear Jef Faridi I'm facing etl integration error after the migration of DCO

Before we were running both DCO and DCE in one server and now we had space issues, So we migrated DCO to new server and etl integration stopped working with showing some errors, refer to the below image

Pls support and suggest

 

Thank you.

(CID:119048274)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 12
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:16 PM . Last Modified: ‎2024-04-08 12:41 AM

0 Likes
0
1387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:16 PM . Last Modified: ‎2024-04-08 12:41 AM

Jef Faridi Even though i restarted all the integration's twice but still after some time it gets stop and displays the error message

(CID:119048283)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:16 PM . Last Modified: ‎2024-04-08 12:41 AM

0 Likes
0
1387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:16 PM . Last Modified: ‎2024-04-08 12:41 AM

Hi Wassem,

Would it possible to ask for the server logs (can be downloaded from webmin interface, StuxureWare DC Operation > Download Log Files > Download log files). I will send you an invite to my =S= box shortly, so the dat dat can be shared safely with me, thanks.

Kind regards

(CID:119048317)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:16 PM . Last Modified: ‎2024-04-08 12:41 AM

0 Likes
0
1387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:16 PM . Last Modified: ‎2024-04-08 12:41 AM

Dear Jef Faridi

Yeah, i have already downloaded the latest log files.

send me an invite i will share with you.

Thanks for the support

 

(CID:119048325)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:16 PM . Last Modified: ‎2024-04-08 12:41 AM

0 Likes
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:16 PM . Last Modified: ‎2024-04-08 12:41 AM

Jef Faridi check your box folder i have shared the log files

Thank you

(CID:119048359)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:16 PM . Last Modified: ‎2024-04-08 12:41 AM

0 Likes
0
1387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:16 PM . Last Modified: ‎2024-04-08 12:41 AM

Thanks Wassem,

I will get back to you as soon as possible,

Kind regards

(CID:119048365)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:16 PM . Last Modified: ‎2024-04-08 12:41 AM

0 Likes
5
1387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:16 PM . Last Modified: ‎2024-04-08 12:41 AM

Hi Waseem

From the log files it seems the ETL integrations fail on the following error:

Could not read from "file:///data/pentaho/import/DCEVirtualSensors.kjb" because it is a not a file.

You might be able to find the file and others belonging to the integration in the folder:

/data/pentaho_restore/import

They should be moved to the folder:

/data/pentaho/import
With DCE integrations you might also have to reinstall the DCE certificates in the server's Java keystore for the integration to work when running them on a new server.
Regards,
Ulrik

(CID:119048462)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:16 PM . Last Modified: ‎2024-04-08 12:41 AM

In response to DCIM_Support
0 Likes
0
1387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:16 PM . Last Modified: ‎2024-04-08 12:41 AM

Thanks for the reply Ulrik Jørgensen

Jef Faridi So it seems there is an problem but how to solve this completely what i have to do, can i get the complete detail/steps.

Jef pls support this is critical case.

(CID:119048505)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:16 PM . Last Modified: ‎2024-04-08 12:41 AM

In response to DCIM_Support
0 Likes
0
1387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:16 PM . Last Modified: ‎2024-04-08 12:41 AM

Hi Waseem,

I will contact you shortly (by direct email), thanks.

Kind regards

(CID:119048537)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:17 PM . Last Modified: ‎2024-04-08 12:41 AM

In response to DCIM_Support
0 Likes
0
1387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:17 PM . Last Modified: ‎2024-04-08 12:41 AM

Thank you. Jef Faridi

(CID:119048541)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:17 PM . Last Modified: ‎2024-04-08 12:41 AM

In response to DCIM_Support
0 Likes
0
1387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:17 PM . Last Modified: ‎2024-04-08 12:41 AM

Jef Faridi Dear Jef

As requested I've shared the updated log files on same box folder

Thank you very much for your support

(CID:119048989)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:17 PM . Last Modified: ‎2024-04-08 12:41 AM

In response to DCIM_Support
0 Likes
0
1387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:17 PM . Last Modified: ‎2024-04-08 12:41 AM

Many thanks Waseem,

I'm downloading the files at the moment, thanks.

Kind regards

(CID:119048995)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:17 PM . Last Modified: ‎2023-10-22 01:58 AM

0 Likes
0
1387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:17 PM . Last Modified: ‎2023-10-22 01:58 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore