Posted: 2020-07-02 09:38 AM . Last Modified: 2024-04-10 01:09 AM
I am trying to model a 125kW downflow CRAC but the software seems to limit the cooling to 99.9 kW.
Is there a way around this or a different way to model it?
(CID:93193609)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 09:38 AM . Last Modified: 2024-04-10 01:09 AM
Which version of DCO are you using? On my 7.4 there doesn't seem to be any (practical) limitation.

(CID:93193613)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 09:39 AM . Last Modified: 2024-04-10 01:09 AM
Christian,
I am also on 7.4 and when I try to enter 125kw, it changes the number to 12.5
When I try to increase the number manually by pressing the up arrow, it stops at 100.00

(CID:93193616)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 09:39 AM . Last Modified: 2024-04-10 01:09 AM
(CID:93193630)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 09:39 AM . Last Modified: 2024-04-10 01:09 AM
Hi,
I believe this is limited to 100 kW. There is an enhancement request in the system for this.
Work around: add the device/Downflow CRAC to your room, and then change/set the "Cooling capacity".
Regards,
Breda
(CID:93193620)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 09:39 AM . Last Modified: 2023-10-31 10:55 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.