Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Please select a country to continue with beta search.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 09:43 PM . Last Modified: 2024-04-04 03:34 AM
(CID:133371543)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 09:43 PM . Last Modified: 2024-04-04 03:34 AM
Hi, there is a workaround for this problem. Please go to
Device – SNMP device….. – Device file transfer settings and add there additional "file transfer settings": with correct username, password and specific address IP for RC unit. Make sure that you will choose protocol: FTP Only
After please do usual "request device scan".
It helped me with 2 customer in last 2 weeks.
(CID:134023943)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 09:43 PM . Last Modified: 2024-04-04 03:34 AM
Dear Fiaz Ahmed,
On this problem here on EcoStruxure IT there are many topics with answers.
To avoid this problem, you must follow the instructions FA177004 StruxureWare Data Center Expert message "Device status may be inaccurate due to attempt to transfer ....
If you have any more questions, please ask.
With respect.
(CID:133371577)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 09:43 PM . Last Modified: 2024-04-04 03:34 AM
Hi, there is a workaround for this problem. Please go to
Device – SNMP device….. – Device file transfer settings and add there additional "file transfer settings": with correct username, password and specific address IP for RC unit. Make sure that you will choose protocol: FTP Only
After please do usual "request device scan".
It helped me with 2 customer in last 2 weeks.
(CID:134023943)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 09:43 PM . Last Modified: 2024-04-04 03:34 AM
Dear Fiaz Ahmed,
Tell us, please, have you solved this question or not?
With respect.
(CID:134026527)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 09:43 PM . Last Modified: 2024-04-04 03:34 AM
No Not Yet !!
(CID:134679888)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 09:44 PM . Last Modified: 2023-10-22 01:56 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.