Hi Team,
One of our customer has integrated DCE to their OSS NMS where our DCE forward all alert traps to the NMS. This is to track and a repository for all alert history in their data center. Now the question is, if our DCE lost its communication to the network, will it re-send all alerts to their OSS that when the network communication had been restored.
Otherwise is there anyway we can check what alerts had not been send? and manually synchronize?
Thanks and regards,
Rayson
(CID:102925110)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 03:45 PM . Last Modified: 2024-04-09 03:03 AM
Hi Rayson,
E-mails may be resent if the target is unreachable. SNMP will not be resent if the target is unreachable. The reason for SNMP not re-sending is that it uses UDP and not TCP. UDP requires no connection / handshake between the 2 systems. The data is simply sent to the IP and receipt is not verified. Please remember also that you can set the system to repeat alarms until cleared.
Steve
(CID:102925150)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 03:45 PM . Last Modified: 2024-04-09 03:03 AM
Hi Rayson,
E-mails may be resent if the target is unreachable. SNMP will not be resent if the target is unreachable. The reason for SNMP not re-sending is that it uses UDP and not TCP. UDP requires no connection / handshake between the 2 systems. The data is simply sent to the IP and receipt is not verified. Please remember also that you can set the system to repeat alarms until cleared.
Steve
(CID:102925150)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 03:45 PM . Last Modified: 2024-04-09 03:03 AM
Thanks Steve, you have always been helpful. Cheers!
(CID:102925182)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 03:45 PM . Last Modified: 2023-10-31 10:55 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.