Device alarms notification policy

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Device alarms notification policy
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
jzurera
Lt. Commander jzurera
Lt. Commander

Posted: ‎2020-05-04 06:23 AM

0 Likes
9
3223
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-04 06:23 AM

Device alarms notification policy

Hi team,

 

I would like to know if it is possible to change the default notification policy in Device Alarms in DCE. In thresholds alarms it is possible, but in device alarms I do not see how to change the default notification policy.

 

Regards

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Cory_McDonald
Admiral Cory_McDonald Admiral
Admiral

Posted: ‎2020-05-05 08:26 AM

In response to jzurera
0 Likes
1
3188
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-05 08:26 AM

@jzurera,

 

You can move a device out of the default notification policy to another if you want, but just keep in mind that all Device Alarm Configurations, for that device, move with it.  If you want to be notified of all alarms on some devices, you can move the "Devices" into that notification policy and set up actions.  The reason that all of the devices are in the default notification policy is because that is the default option when discovering a device.

 

There is two ways to move devices to a new notification policy:

  1. Alarm Configuration Perspective > Navigation Pane > Right-click on device > Change Device Alarm Notification Policy > Choose new policy.
  2. Alarm Configuration Perspective > Notification Policies Pane > Right-click on Policy (you want devices to be in) > Edit > Devices Tab (bottom section) > Choose Devices... > Check the boxes for the devices you want to be part of this policy.

 

Following these steps will allow you to separate out your Device Alarm Configurations, by device, into different notification policies, rather than them all being within the Default Policy with no actions.

 

Kind Regards,

Cory

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
Cory_McDonald
Admiral Cory_McDonald Admiral
Admiral

Posted: ‎2020-05-04 07:14 AM

0 Likes
8
3215
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-04 07:14 AM

Hello jzurera,

 

It is not currently possible to make a different notification policy in DCE the default policy (grayed out).  You can rename the default policy, and use it like any other notification policy, but it will still always be the default policy.  You can manage what actions are within it and what Thresholds or Devices (Device Alarm Configurations) are in it, just like any other policy though.

 

Regards,

Cory

Reply

Link copied. Please paste this link to share this article on your social media post.

jzurera
Lt. Commander jzurera
Lt. Commander

Posted: ‎2020-05-04 09:36 AM

In response to Cory_McDonald
0 Likes
7
3210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-04 09:36 AM

HI,

but I have a notification policy configured for threshold alarms and I would like to assign this policy to only one device alarm. If I configure the default notification policy it will affect to all the device alarms, and I only want to receive emails for a specific device alarm.

 

Is it possible?

Reply

Link copied. Please paste this link to share this article on your social media post.

ATrabert
Lt. Commander ATrabert Lt. Commander
Lt. Commander

Posted: ‎2020-05-04 11:04 AM

In response to jzurera
1 Like
5
3205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-04 11:04 AM

Unfortunately as you've already found out, no you cannot assign a notification policy to an individual device alarm, it's all or nothing.

 

What is the alarm specifically?  There may be another way to get it using threshold alarms, but it depends.

Reply

Link copied. Please paste this link to share this article on your social media post.

Cory_McDonald
Admiral Cory_McDonald Admiral
Admiral

Posted: ‎2020-05-04 11:09 AM

In response to jzurera
0 Likes
0
3204
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-04 11:09 AM

Hello jzurera,

 

All device level configurations (alarms) are tied to the device and they can't split out.  You can look into making custom thresholds if there is a sensor value that can be used to determine if the condition exists or not.  This custom threshold can then be put into your separate policy from the device alarm configurations.

 

Regards,

Cory

Reply

Link copied. Please paste this link to share this article on your social media post.

jzurera
Lt. Commander jzurera
Lt. Commander

Posted: ‎2020-05-05 01:42 AM

In response to ATrabert
0 Likes
4
3197
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-05 01:42 AM

Hi,

 

our customer had a problem in a compressor inside a cooling machine and we have seen that there was a device alarm that informed of this error, but it did not have any action alarm configured because it was inside the default notification policy.

 

We have checked the sensors of this cooling machine and we have seen that the temperature of the compressor was very high during this fault. So we could configure a threshold of this sensor but we have another problem, the normal temperature of this sensor is above 60ºC, and during the alarm was more than 80ºC, and the maximum temperature value that DCE admits for a threshold temperature alarm is 50ºC. So we cannot use this sensor.

 

Regards

Reply

Link copied. Please paste this link to share this article on your social media post.

Cory_McDonald
Admiral Cory_McDonald Admiral
Admiral

Posted: ‎2020-05-05 05:52 AM

In response to jzurera
0 Likes
3
3193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-05 05:52 AM

Hello @jzurera,

 

Thank you for the additional information.  I am curious as to why your device is not within a notification policy that has actions, whether that be the default or another, to catch and send these Device Alarm Configurations.  You could create different actions for different severities, if you were concerned with receiving too many alarms.  You can also reclassify these alarms to different severities if you wanted to limit it down further to which ones you considered in each category: failure, critical, error, warning, and Informational.

 

Regards,

Cory

Reply

Link copied. Please paste this link to share this article on your social media post.

jzurera
Lt. Commander jzurera
Lt. Commander

Posted: ‎2020-05-05 08:04 AM

In response to Cory_McDonald
0 Likes
2
3190
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-05 08:04 AM

Hi @Cory_McDonald 

 

I have seen that I cannot assign a custom notification policy to preconfigured device alarms, only the default notification policy is configured and cannot be disabled. If I activate actions for the default policy, all the devices with preconfigured device alarms wil be affected because all of them are inside the default notification policy.

 

We have configured the actions with a customized notification policy assigned to threshold alarms. If we could configure the temperature above 50ºC it would be enough and we would not need the device alarms.

Regards

Reply

Link copied. Please paste this link to share this article on your social media post.

Cory_McDonald
Admiral Cory_McDonald Admiral
Admiral

Posted: ‎2020-05-05 08:26 AM

In response to jzurera
0 Likes
1
3189
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-05 08:26 AM

@jzurera,

 

You can move a device out of the default notification policy to another if you want, but just keep in mind that all Device Alarm Configurations, for that device, move with it.  If you want to be notified of all alarms on some devices, you can move the "Devices" into that notification policy and set up actions.  The reason that all of the devices are in the default notification policy is because that is the default option when discovering a device.

 

There is two ways to move devices to a new notification policy:

  1. Alarm Configuration Perspective > Navigation Pane > Right-click on device > Change Device Alarm Notification Policy > Choose new policy.
  2. Alarm Configuration Perspective > Notification Policies Pane > Right-click on Policy (you want devices to be in) > Edit > Devices Tab (bottom section) > Choose Devices... > Check the boxes for the devices you want to be part of this policy.

 

Following these steps will allow you to separate out your Device Alarm Configurations, by device, into different notification policies, rather than them all being within the Default Policy with no actions.

 

Kind Regards,

Cory

Reply

Link copied. Please paste this link to share this article on your social media post.

jzurera
Lt. Commander jzurera
Lt. Commander

Posted: ‎2020-05-06 06:27 AM

In response to Cory_McDonald
0 Likes
0
3182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-06 06:27 AM

Thank you @Cory_McDonald , I didn't know that I could change the notification policy from the navigation menu. I had always changed the notification policy in the right panel of Threshold Alarm Configuration, and this option does not appear for Device Alarms Configuration tab.

 

This is very useful.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore