Posted: 2020-07-02 10:53 PM . Last Modified: 2024-04-09 01:18 AM
Hello Guys,
I have a problem of connecting more than 1 uniflair unit.
At the site their are 5 units each with pcoweb and all what I can detect when I add a new device in DCE is the first unit only.
what could be done here ? And should all the units be LAN connected together or Each can be stand alone ?
(CID:105461834)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 10:53 PM . Last Modified: 2024-04-09 01:18 AM
As far as I know, each Uniflair unit's pcoweb NIC card should be configured with an IP address in order to connect to DCE software via SNMP.

(CID:105461837)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 10:53 PM . Last Modified: 2024-04-09 01:18 AM
Hi Pierre,
That is correct all the units will require separate IP addresses.
(CID:105461859)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 10:53 PM . Last Modified: 2024-04-09 01:18 AM
Pierre,
Start with some basic troubleshooting.
Are all the units able to be "pinged"
Do you have an different IP assigned to each individual Unit?
Are you able to reach individual units HTTP pages via a web browser?
Do you have the correct SNMP settings on each individual Unit?
When doing the discovery are you using the correct IP & SNMP info?
Once you are able to say YES to the above then you should be able to add all of the individual units into DCE .
(CID:105461911)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 10:53 PM . Last Modified: 2023-10-31 10:53 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.