Detected an unauthorized user attempting to access the SNMP interface

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Detected an unauthorized user attempting to access the SNMP interface
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:47 AM . Last Modified: ‎2024-04-08 11:52 PM

0 Likes
9
13612
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:47 AM . Last Modified: ‎2024-04-08 11:52 PM

Detected an unauthorized user attempting to access the SNMP interface

We have couple of and different type of APC ATS/UPS/PDU device with network communication. E-mail notification has been configured to send alerts in case of a problem.

Corporate network has been scanned with different tools which are mostly using SNMP protocol. APC devices are flooding recipients with e-mail alerts such as the following:

Detected an unauthorized user attempting to access the SNMP interface from <IP address>

Devices are also monitored by DCE.

How can I configure devices to not send e-mail alerts because of network discovery scans?

I tried the following changes in devices configuration without any success:

  1. Administration -> Network -> SNMPv1 -> access control: public community name used by scanning tool and also added the server IP to NMS IP/Host Name
  2. Administration -> Notification -> SNMP Traps -> Trap receiver : trap generation has been enabled and scan server IP added to NMS IP/Host Name. Public SNMPv1 has been used.

(CID:106207646)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:48 AM . Last Modified: ‎2024-04-08 11:52 PM

0 Likes
0
13601
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:48 AM . Last Modified: ‎2024-04-08 11:52 PM

Hi Mate,

Editing events in DCE is not always that easy. I suggest manually editing one device using it's UI as noted above. When you do this, make note of the event number. For this one, I noted the following:

Detected an unauthorized user attempting to access the Control Console interface.[0x0005]

 Once you've done that, go to APC SNMP device configuration.

Choose standard device configuration settings.

Choose configure devices or create a template.

Find the device you've just configured, select it and choose retrieve device settings.

Choose your destination devices.

Next, make sure all settings are unchecked. To be sure, maybe even select all and unselect all.

Click the > next to advanced settings, then the > next to event action config

You should see the events with the codes (not names) but since you noted the code when configuring it, this should not be an issue:

Select the proper event (E0005 in this case) and hit next.

At this point, either save the template or configure the devices.

 

Steve

 

 

 

(CID:106207700)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:47 AM . Last Modified: ‎2024-04-08 11:52 PM

0 Likes
6
13600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:47 AM . Last Modified: ‎2024-04-08 11:52 PM

Hi Mate,

 

Your first best bet would be to stop the scanning with incorrect credentials. If you must turn it off, verify if it is coming from the network card in the device or StruxureWare. If it is the device, you can use the following menus on a 6.x firmware to configure specific events. Choose "By Event":

 

For this specific event, choose security:

You then have a number of options:

 

If you're using StruxureWare but getting events from the device, you can mass configure devices to exclude that event. If you're not using StruxureWare, you can configure one device then download the config.ini file from that device. You can then upload just that section to the other APC devices. K-base FA176542 may be helpful if you're not sure how to do that.

 

Thanks,

Steve

 

 

(CID:106207653)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:48 AM . Last Modified: ‎2024-04-08 11:52 PM

In response to DCIM_Support
0 Likes
0
13600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:48 AM . Last Modified: ‎2024-04-08 11:52 PM

Hi Steven,

Thanks for your quick response. I know that I can turn off notification and/or log for that particular event however from do it DCE in batch was new for me. I would like to use this option at last.

You mentioned credential but what kind of credential is in use if we are talking about SNMP v1/v2?

Scan is using the "public" SNMP community name.

(CID:106208859)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:48 AM . Last Modified: ‎2024-04-08 11:52 PM

In response to DCIM_Support
0 Likes
0
13600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:48 AM . Last Modified: ‎2024-04-08 11:52 PM

Mi Mate, If a system is scanning using just the one community name that is turned on in the NMC AND that community name does not have an IP associated with it, you should not get that error. Note that the community name config on the NMC can have an associated NMS IP. Most SNMP scans from other systems will scan an entire segment with one community name, then again with another, and so on. If you look at the logs on the NMC, it will tell you what system is doing this poll...just in case it is a system you're not expecting it from. Steve

(CID:106208853)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:48 AM . Last Modified: ‎2024-04-08 11:52 PM

In response to DCIM_Support
0 Likes
0
13601
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:48 AM . Last Modified: ‎2024-04-08 11:52 PM

And the default 0.0.0.0 IP at SNMP setting means that NMC can accept request from every IP address? In that case I do not really understand how DCE monitoring APC devices via SNMP. In that case devices are not generating alerts.

(CID:106208862)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:48 AM . Last Modified: ‎2024-04-08 11:52 PM

In response to DCIM_Support
0 Likes
0
13601
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:48 AM . Last Modified: ‎2024-04-08 11:52 PM

Hi Mate, Yes, 0.0.0.0 means any system can use that community name to poll that device. I'm unsure what you mean with your second statement. In that case devices are not generating alerts. This is indicating you're NOT getting messages? Are you saying the event is saying that DCE's IP is the one the device is reporting as causing the error? If so, do you have multiple discoveries in DCE with different community names that periodically run? I really can't say. What I can suggest if you need someone to walk you through it is if you call tech support, you can often work with the support people and get a webex going where the reps can actually see your configuration and can more easily understand what's happening. Steve

(CID:106208852)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:48 AM . Last Modified: ‎2024-04-08 11:52 PM

In response to DCIM_Support
0 Likes
0
13601
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:48 AM . Last Modified: ‎2024-04-08 11:52 PM

Oh yeah, I understand it. Even if I create a community string which will be match with scan setting there is other couple of string which fails during the attempt. For permanent solution I can see only the event disable. How can I do that from DCE? I select APC SNMP Device Configuration from Device menu and retrive on device configuration and select another one the following possibilities are available:

24-06-2016 16-53-00.png

(CID:106208860)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:48 AM . Last Modified: ‎2024-04-08 11:52 PM

In response to DCIM_Support
0 Likes
0
13601
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:48 AM . Last Modified: ‎2024-04-08 11:52 PM

We have this same issue. Our network team uses a software with the correct SNMP strings however the APC devices spew 'Unauthorized User' emails. After trying to figure out why, I just resorted to turning them off. The problem with that is new devices added by the IT department... they don't always push the template to the device and then my inbox gets filled up. You also can not easily update the template which leads me to create multiple templates for one device. You can only edit a setting set in the template, any new changes require a new template. Great idea, rough execution. I would still prefer the templates though.

(CID:106208855)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:48 AM . Last Modified: ‎2024-04-08 11:52 PM

0 Likes
0
13602
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:48 AM . Last Modified: ‎2024-04-08 11:52 PM

Hi Mate,

Editing events in DCE is not always that easy. I suggest manually editing one device using it's UI as noted above. When you do this, make note of the event number. For this one, I noted the following:

Detected an unauthorized user attempting to access the Control Console interface.[0x0005]

 Once you've done that, go to APC SNMP device configuration.

Choose standard device configuration settings.

Choose configure devices or create a template.

Find the device you've just configured, select it and choose retrieve device settings.

Choose your destination devices.

Next, make sure all settings are unchecked. To be sure, maybe even select all and unselect all.

Click the > next to advanced settings, then the > next to event action config

You should see the events with the codes (not names) but since you noted the code when configuring it, this should not be an issue:

Select the proper event (E0005 in this case) and hit next.

At this point, either save the template or configure the devices.

 

Steve

 

 

 

(CID:106207700)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:48 AM . Last Modified: ‎2023-10-31 10:53 PM

0 Likes
0
13600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:48 AM . Last Modified: ‎2023-10-31 10:53 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore