New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Data center expert email problem
EcoStruxure IT Forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-2611:50 PM
Data center expert email problem
The Netbotz system that our customer is using shows the incoming errors.
Data center expert shows Netbotz errors, but data center experts does not e-mail errors from Netbotz.
Sane Data Center Experts has connected UPS Systems , Cooling Units and other data center products and sending email without any problems Our problem ise only Netbotz alarms .
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-2712:06 AM
If you are using the Netbotz appliance 300-500 series, then the email notification is triggered from the Netbotz appliance itself not by DCE when alarm occurs as per the notification profile configured in Netbotz appliance.
Therefore, please configure the email notification as per the below k-base document and see if you are getting the email notification from Netbotz.