Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

DDF for ASCO 7000 Series ATS

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DDF for ASCO 7000 Series ATS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 02:12 PM . Last Modified: ‎2024-04-08 01:23 AM

0 Likes
14
2704
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:12 PM . Last Modified: ‎2024-04-08 01:23 AM

DDF for ASCO 7000 Series ATS

In January I posted about a threshold configuration issue that I had with DCE for voltage readings (normal VCA) on ASCO 7000 Series ATS switches.  The issue is that the sensor was providing a reading in the "thousands" vs. the "hundreds"  (example 208.0 Volts appears as 2080.0 volts)  I got a response about it being a scaling factor used in DDF.  I was provided with a modified DDF file that was suppose to fix my issue.  I followed the instructions to import the updated DDF into the tool and it has not fixed the issue.  Would really like a fix that would correct this problem.  Thank you

(CID:114234246)

Labels
  • Labels:
  • Data Center Expert
  • DDF
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 14
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 02:12 PM . Last Modified: ‎2024-04-08 01:23 AM

0 Likes
0
2704
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:12 PM . Last Modified: ‎2024-04-08 01:23 AM

Hello Scott,

 

The updated DDF sent to you from the zendesk support. Please test it and reply if it works.

 

Thanks and Regards,

Mohan Gowda

(CID:114234304)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 02:12 PM . Last Modified: ‎2024-04-08 01:23 AM

0 Likes
0
2704
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:12 PM . Last Modified: ‎2024-04-08 01:23 AM

Hello Mohan -

 

I've extracted the .xml file from the zip file and have attempted to import it into the tool and I receive a Status of "Incorrect File Type" in the Select DDF Files screen of the import process.  I can not proceed further at this point.

(CID:114820896)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 02:12 PM . Last Modified: ‎2024-04-08 01:23 AM

0 Likes
0
2704
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:12 PM . Last Modified: ‎2024-04-08 01:23 AM

Hi scott.walter,

And it is possible to look on above the specified DDF-file? If of course you doesn't object, I will be able probably to help.

With best regards.

(CID:114820902)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 02:13 PM . Last Modified: ‎2024-04-08 01:23 AM

0 Likes
0
2704
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:13 PM . Last Modified: ‎2024-04-08 01:23 AM

I believe the conflict might be the version number possibly because the last DDF I received for this was also "version 2", and that version is already updated into the tool both the DDF I received in January and recently are .xml files.  Is it possible to have the last file I received on 3/20 with a different numerical version and give that a try before moving on?

(CID:114820951)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 02:13 PM . Last Modified: ‎2024-04-08 01:23 AM

0 Likes
0
2704
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:13 PM . Last Modified: ‎2024-04-08 01:23 AM

Perhaps, but it seems to me, a problem not in versions of the DDF-file. It is difficult for me to judge it now without DDF-file.

With best regards.

(CID:114820957)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 02:13 PM . Last Modified: ‎2024-04-08 01:23 AM

0 Likes
0
2704
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:13 PM . Last Modified: ‎2024-04-08 01:23 AM

is the ddf modbus or snmp?  

 

Any time I've seen the "incorrect file type" error, its because I tried to add the modbus ddf as an snmp ddf or a snmp ddf as a modbus ddf.

 

I would double check that you are adding it as the correct type,

eg device -->snmp device comm settings–>device definition files

or 

device–>modbus device comm settings --> device definition files

(CID:114821352)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 02:13 PM . Last Modified: ‎2024-04-08 01:22 AM

0 Likes
0
2704
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:13 PM . Last Modified: ‎2024-04-08 01:22 AM

Thanks Andrew - that seem to solve the issue of "incorrect file type" however after importing the file and logging in and out of the application I still get the 1000 reading for ATS VCA sensor value vs. the 100 reading I was hoping for, does anyone know if that's typical and the default setting?

(CID:114821401)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 02:13 PM . Last Modified: ‎2024-04-08 01:22 AM

0 Likes
0
2704
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:13 PM . Last Modified: ‎2024-04-08 01:22 AM

If you're ok with losing some sensor history, you can delete and re-add the device.  I've had to do that in the past with a scaling issue.  

 

You may also want to compare the two ddfs using a text editer (eg notepad ++), find the sensor in question and verify that the scaling factor was changed.

 

In the example below, DCE is multiplying the L2 Current IA sensor by 0.001 to convert the value.


_L2_CURRENT_IA



Function_3_Reg_1

0.001 <-- this is the scaling factor

 

if they didn't fix it, send it back to the ddf team so they can correct and send you an updated ddf.   While its a relatively quick fix, I don't recommend making these changes yourself.

(CID:114821416)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 02:13 PM . Last Modified: ‎2024-04-08 01:22 AM

0 Likes
0
2704
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:13 PM . Last Modified: ‎2024-04-08 01:22 AM

scott.walter Hi Scott, 

Can you please send the  list/screenshot of sensor values that you want to see the scaled down values. I can make the changes and send an updated DDF to you.

 

Thanks and Regards,

Mohan Gowda

(CID:114821441)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 02:13 PM . Last Modified: ‎2024-04-08 01:22 AM

0 Likes
0
2704
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:13 PM . Last Modified: ‎2024-04-08 01:22 AM

Hi scott.walter,

About above the specified multiplier it is possible to see visually, for example, here: 

With best regards.

(CID:114821478)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 02:13 PM . Last Modified: ‎2024-04-08 01:22 AM

0 Likes
0
2704
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:13 PM . Last Modified: ‎2024-04-08 01:22 AM

Mohan Gowda - attached is a PNG file that shows Normal VCA as 2,113.0V and I'm thinking it should show it as 211.3V unless that is not correct as to how the software should report it.

(CID:114821533)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 02:14 PM . Last Modified: ‎2024-04-08 01:22 AM

0 Likes
1
2704
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:14 PM . Last Modified: ‎2024-04-08 01:22 AM

scott.walter 

Hello Scott,

I have sent updated DDF from Zendesk support. I believe that would solve the problem. Please test it and let us know if you have any issues.

Thanks and Regards,

Mohan Gowda

(CID:115345130)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 02:14 PM . Last Modified: ‎2024-04-08 01:22 AM

In response to DCIM_Support
0 Likes
0
2704
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:14 PM . Last Modified: ‎2024-04-08 01:22 AM

Hello Mohan -

 

This last DDF seems to have fixed the issue.  I noticed there are some additional sensor value readings on this DDF than the one I had, this will not affect any alert threshold settings will it?

 

Thanks,

 

Scott

(CID:115345134)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 02:14 PM . Last Modified: ‎2023-10-22 01:48 AM

0 Likes
0
2703
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:14 PM . Last Modified: ‎2023-10-22 01:48 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore