DCO snyc problem with DCE

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCO snyc problem with DCE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:07 PM . Last Modified: ‎2024-04-08 12:19 AM

0 Likes
6
971
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:07 PM . Last Modified: ‎2024-04-08 12:19 AM

DCO snyc problem with DCE

I am running DCE 7.4.1 and DCO 8.0.1 which are in connection thru configured external systems in DCO. Here is the settings:

 

The problem is that in DCO I can see alerts which are not present in DCE. Of course I gave enough time for update. Here is an example from the short summary info from the bottom of the client softwares:

I can see 8 alerts in DCO and 1 warning while in DCE I have only 6 errors.

 

(CID:120134824)

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:07 PM . Last Modified: ‎2024-04-08 12:19 AM

0 Likes
4
971
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:07 PM . Last Modified: ‎2024-04-08 12:19 AM

Hi Mate

Operation gets alarms in two ways from the Expert:

1) Expert pushes alarms via web service on the Operation server (live updates)

2) Every hour Operation does a full fetch of alarms

The callback server is used in scenario 1, and the setting contains the information Experts needs in order to call Operation. From your screen shot it seems Expert will call Operation on port 80, but default for Operations 8.x is to only accept secure connections on port 443. Is Operation allowing insecure access on port 80?

If not you can change the setting to "Use encryption" - then you will need to import the Operation server certificate into Expert so Expert is be able to connect to Operation. You can see how to do that here: Configuring StruxureWare Data Center Expert integration.

Regards,

Ulrik

(CID:120134850)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:07 PM . Last Modified: ‎2024-04-08 12:19 AM

In response to DCIM_Support
0 Likes
0
971
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:07 PM . Last Modified: ‎2024-04-08 12:19 AM

Hi Ulrik,

Thank you for your answer. I did the certificate "exchange" between DCO and DCE but it problem is still persist.

Anyway I just realized that something is wrong in DCO at external systems. I have more added systems in external system config then at Device Association, so I am not able to associate devices. See:

(CID:120135700)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:08 PM . Last Modified: ‎2024-04-08 12:18 AM

In response to DCIM_Support
0 Likes
0
971
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:08 PM . Last Modified: ‎2024-04-08 12:18 AM

Hi Mate

Note: after you have added the Operation certificate to Expert and updated the configuration to use encryption and port 443, it might take up to an hour for Operation to show the right data. Operation would have to do a full fetch (done every hour) and then start receiving the smaller changes before being up-to-date. If you are still seeing the issue, perhaps you could share the Operation and Expert log files?

Regarding the UCS integrations - could you try to open the configurations in Operation (so it shows the configuration parameters like hostname, etc.), press OK, and then save changes. That should trigger the UCS jobs again. If they devices still do not show up in the view I might need the Operation server logs in order to debug.

Regards,

Ulrik

 

(CID:120135703)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:08 PM . Last Modified: ‎2024-04-08 12:18 AM

In response to DCIM_Support
0 Likes
0
971
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:08 PM . Last Modified: ‎2024-04-08 12:18 AM

Hi Ulrik,

I waited more than 1 day after certificate change. I already tried the "double check" the UCS Manager settings and saved changes at the end without any luck.

I uploaded the logs to a website just please provide an email address because I have to grant access and send invitation to that mail. The log file is large: almost 1GB

Regads,

Mate

(CID:120136472)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:08 PM . Last Modified: ‎2024-04-08 12:18 AM

In response to DCIM_Support
0 Likes
0
971
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:08 PM . Last Modified: ‎2024-04-08 12:18 AM

Hi Mate

My e-mail address is ulrik.joergensen@schneider-electric.com. When I have downloaded the log files, I will get back to you.

Regards,

Ulrik

(CID:120136500)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:08 PM . Last Modified: ‎2023-10-22 01:46 AM

0 Likes
0
971
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:08 PM . Last Modified: ‎2023-10-22 01:46 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore