Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

DCO down and does not start

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCO down and does not start
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 02:26 PM . Last Modified: ‎2024-04-05 02:38 AM

0 Likes
7
1843
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:26 PM . Last Modified: ‎2024-04-05 02:38 AM

DCO down and does not start

Hello Team,

I have a problem...

We have a installation with two environments, Production and Preproduction, both in disaster recovery mode. So we have 4 virtual machines running with DCO 8.2.0.

Today both environments are not working. We have checked the status and the aplication is down:

 

I have rebooted the nodes and the problem does not disappear. Also I have tried to restore from the last backup and I got this error:

 

As you can see the machine has IP 172.20.17.159 but then in the log, it tries to find localhost on IP 172.17.34.189. That IP does not belong to any DCO machine, so I do not know why It appears here.

Finally I tried to promote the secondary node to primary but it falso failed due to the same problem.

Do you know what could be happening? I have the same error in the four virtual machines with different IPs.

I would like to attach the server's logs, but they are empty when I download them. I receive all these errors during the process:


StruxureWare Data Center Operation - Download Log Files
 

 


Creating staging directory.
Location '/tmp/logs/ito' did not exist. Creating it.
Retrieving ITO log files.
Unable to retrieve log files from the ITO server(s)
Gathering logfiles on host: localhost
Retrieving logfiles from host: localhost
non zero exit value(1) for command: export LANG=en_US.UTF-8; sudo -u dcoplat scp -r -o LogLevel=Error -r localhost:"/tmp/logs.tar.gz" /tmp/logs/localhost.tar.gz

ssh: connect to host localhost port 22: Connection refused 

Unable to copy /tmp/logs.tar.gz from localhost to /tmp/logs/localhost.tar.gz.
Output: ssh: connect to host localhost port 22: Connection refused 

Creating staging dir.
Location '/tmp/logs/localhost' did not exist. Creating it.
non zero exit value(2) for command: export LANG=en_US.UTF-8; tar -zxf /tmp/logs/localhost.tar.gz -C /tmp/logs/localhost

tar (child): /tmp/logs/localhost.tar.gz: Cannot open: No such file or directory
tar (child): Error is not recoverable: exiting now
tar: Child returned status 2
tar: Error is not recoverable: exiting now

Unable to untar log files from localhost to log file staging area (/tmp/logs)
Removing file '/tmp/logs/localhost.tar.gz'
Unable to cleanup log tar.
Gathering performance graphs for host: localhost
Retrieving performance graphs for host: localhost
non zero exit value(1) for command: export LANG=en_US.UTF-8; sudo -u dcoplat scp -r -o LogLevel=Error -r localhost:"/tmp/graphs.tar.gz" /tmp/logs/localhost-graphs.tgz

ssh: connect to host localhost port 22: Connection refused 

Unable to copy /tmp/graphs.tar.gz from localhost to /tmp/logs/localhost-graphs.tgz.
Output: ssh: connect to host localhost port 22: Connection refused 

Location '/tmp/logs/localhost/graphs' did not exist. Creating it.
non zero exit value(2) for command: export LANG=en_US.UTF-8; tar -zxf /tmp/logs/localhost-graphs.tgz -C /tmp/logs/localhost/graphs

tar (child): /tmp/logs/localhost-graphs.tgz: Cannot open: No such file or directory
tar (child): Error is not recoverable: exiting now
tar: Child returned status 2
tar: Error is not recoverable: exiting now

Unable to untar /tmp/logs/localhost/graphs to /tmp/logs/localhost-graphs.tgz, failed with 2
Removing file '/tmp/logs/localhost-graphs.tgz'
Compressing log files in /tmp/logs.
Removing temporary files
Done gathering logfiles.
Sending to client. 

(CID:128758911)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 02:26 PM . Last Modified: ‎2024-04-05 02:38 AM

0 Likes
5
1843
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:26 PM . Last Modified: ‎2024-04-05 02:38 AM

Javier, is there some sort of mixup in the hostname or IP address information in the DCO server's /etc/hosts file or in DNS which might cause the mix-up in IP address resolution?

Regards

Greg Sterling

(CID:128759413)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 02:26 PM . Last Modified: ‎2024-04-05 02:38 AM

0 Likes
5
1844
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:26 PM . Last Modified: ‎2024-04-05 02:38 AM

Javier, is there some sort of mixup in the hostname or IP address information in the DCO server's /etc/hosts file or in DNS which might cause the mix-up in IP address resolution?

Regards

Greg Sterling

(CID:128759413)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 02:26 PM . Last Modified: ‎2024-04-05 02:38 AM

In response to DCIM_Support
0 Likes
0
1845
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:26 PM . Last Modified: ‎2024-04-05 02:38 AM

Thank you Greg, it works.

I do not know exactly where the problem is, but after disabling DNS and Search Domains it is working again.

Now I have to investigate that, but DCO is working.

Very helpful.

(CID:128759417)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 02:26 PM . Last Modified: ‎2024-04-05 02:38 AM

In response to DCIM_Support
0 Likes
0
1845
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:26 PM . Last Modified: ‎2024-04-05 02:38 AM

Hi Greg Sterling,

without the DNS server configured DCO works, but we need the DNS for remote backup and also for NTP.

These DNS servers are working with all the organization, only DCO fails.So we think the problem is not located in the DNS servers.

I have just tried to configure once again the DNS server, and DCO crashes. I have downloaded the logs of the server (400 MB).

Can I share this with someone to check it?

Thanks in advance.

(CID:128763068)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 02:26 PM . Last Modified: ‎2024-04-05 02:38 AM

In response to DCIM_Support
0 Likes
0
1843
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:26 PM . Last Modified: ‎2024-04-05 02:38 AM

Hi Javier,

Can you please share the server logs with me (via my box folder), I will send you an invite soon, thanks.

Kind regards

(CID:128763072)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 02:26 PM . Last Modified: ‎2024-04-05 02:37 AM

In response to DCIM_Support
0 Likes
0
1843
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:26 PM . Last Modified: ‎2024-04-05 02:37 AM

Thank you Jef, I have just uploaded the logs in your folder.

(CID:128763093)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 02:26 PM . Last Modified: ‎2024-04-05 02:37 AM

In response to DCIM_Support
0 Likes
0
1844
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:26 PM . Last Modified: ‎2024-04-05 02:37 AM

Hi Javier,

Many thanks for providing the data - it seems you have configuration issue in /etc/hosts - the entry "localhost" is missing. I will also send you a direct email as well, thanks.

Kind regards

(CID:129403970)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 02:27 PM . Last Modified: ‎2023-10-22 01:44 AM

0 Likes
0
1846
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:27 PM . Last Modified: ‎2023-10-22 01:44 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.