DCO User Access Log

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCO User Access Log
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 12:23 PM . Last Modified: ‎2024-04-09 11:52 PM

0 Likes
8
907
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 12:23 PM . Last Modified: ‎2024-04-09 11:52 PM

DCO User Access Log

Does anyone know if there is a simple log file in DCO that shows all access attempts and if they are successful or not, from the Operation and Lab client, webmin and console.

This information is required for our internal auditing process.

(CID:96044826)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 12:23 PM . Last Modified: ‎2024-04-09 11:52 PM

0 Likes
6
907
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 12:23 PM . Last Modified: ‎2024-04-09 11:52 PM

Hi Richard,

Users logging in and logging out are recorded in audit trail, and can be generated via "Analytics Reports" -> "Audit Trail" (new feature in 7.4.5). I guess you knew that already. However the failed user(s) logging attempts might be logged in the server.log file(s).

Kind regards

(CID:96044865)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 12:23 PM . Last Modified: ‎2024-04-09 11:52 PM

In response to DCIM_Support
0 Likes
0
907
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 12:23 PM . Last Modified: ‎2024-04-09 11:52 PM

Hi Jef, it would seem that the Audit Trail report is only available if you have the change module installed, which we don't. Seems a little strange given that you may want access to this report to view the system events even if your not using the change module. Richard

(CID:96044990)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 12:23 PM . Last Modified: ‎2024-04-09 11:52 PM

In response to DCIM_Support
0 Likes
0
907
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 12:23 PM . Last Modified: ‎2024-04-09 11:52 PM

Hi Richard, That's correct, the Change license is required to see the Audit Trail report. I think the audit report has been basically designed for work-orders (requires the Change license). It seems we have already tracked a feature request that system related events could be available having the Operation license only. I have added you to the list of the customers asking for this feature. Kind regards

(CID:96764189)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 12:23 PM . Last Modified: ‎2024-04-09 11:52 PM

In response to DCIM_Support
0 Likes
0
907
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 12:23 PM . Last Modified: ‎2024-04-09 11:52 PM

Thanks Jef

(CID:96764241)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 12:24 PM . Last Modified: ‎2024-04-09 11:52 PM

In response to DCIM_Support
0 Likes
0
907
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 12:24 PM . Last Modified: ‎2024-04-09 11:52 PM

Jef, Could you add CenturyLink to the list as well... We're kicking off an audit here internally as well and would like to be able to see metrics on things like a time-stamp for last time a user logged in. We have the change module but the audit report forces you to pick a single user name.

(CID:106210042)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 12:24 PM . Last Modified: ‎2024-04-09 11:52 PM

In response to DCIM_Support
0 Likes
0
907
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 12:24 PM . Last Modified: ‎2024-04-09 11:52 PM

Hi Wes, Done - it is now added to the case, thanks. Kind regards

(CID:106210084)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 12:24 PM . Last Modified: ‎2024-04-09 11:52 PM

In response to DCIM_Support
0 Likes
0
907
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 12:24 PM . Last Modified: ‎2024-04-09 11:52 PM

Thanks Jef, One quick update from my end... but from what I understand the server.log file contains record of each log in and out. As a temporary workaround I'll try to parse that file to get the summary I'm after. Long term this would be nice to have as a standard report in the GUI.

(CID:106210109)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 12:24 PM . Last Modified: ‎2023-10-31 10:52 PM

0 Likes
0
907
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 12:24 PM . Last Modified: ‎2023-10-31 10:52 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore