DCO U-space report

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCO U-space report
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:28 PM . Last Modified: ‎2024-04-08 01:18 AM

0 Likes
8
1313
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:28 PM . Last Modified: ‎2024-04-08 01:18 AM

DCO U-space report

 

Good day all

Quick observation and i hope there is assistance available.

I ran a simple U-space in DCO and the results did not seem correct and upon investigation i found that DCO counts the "blanking plates" as a device occupying a U-space, which renders the report incorrect. 

In order for me to have a true reflection, i had to remove the blanking plates from the layout, save the changes then re-ran the report to get accurate U-space totals. Moving forward, given that blanking plates are necessary in terms of cooling the entire rack, are there any other methods or reporting methods that i can use to get accurate U-space totals?

 

please forward me a link if possible

Any feedback is greatly appreciated.

Kind regards

(CID:115836827)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:28 PM . Last Modified: ‎2024-04-08 01:18 AM

0 Likes
4
1313
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:28 PM . Last Modified: ‎2024-04-08 01:18 AM

Dear Yusuf,

As far as I know, there is no need to place the blanking panel in DCO Racks layout as DCO by default considers the empty U space are filled with blanking panels. For this reason, there is no need to put the blanking panels in the Racks. This way the DCO will be able to provide the correct U-Space report. 

I hope it helps. 

Regards,

Bala

(CID:115836832)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:28 PM . Last Modified: ‎2024-04-08 01:18 AM

In response to DCIM_Support
0 Likes
0
1313
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:28 PM . Last Modified: ‎2024-04-08 01:18 AM

Thank you Bala for your speedy response

I am aware that if we remove the blanking panels we will have the correct totals, however, was told that best practice is to have the exact replica of our actual layout created in DCO. 

(CID:115836847)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:28 PM . Last Modified: ‎2024-04-08 01:18 AM

In response to DCIM_Support
0 Likes
0
1313
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:28 PM . Last Modified: ‎2024-04-08 01:18 AM

I agree with you. However, there is no genome provided for blanking panel. I hope you might have had customized the blanking panel from any other genome properties. Thats the reason the DCO calculates it as the consumed U-Space if you place it in the Rack layout. There must be some reason on why the blanking panel is not provided in DCO genome. I let the other community experts to suggest on the same. Its not required to place/fill the empty U space(which is occupied by blanking panel physically) in DCO layout as it considers the empty U spaces are filled with blanking panels by default. 

(CID:115836924)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:28 PM . Last Modified: ‎2024-04-08 01:18 AM

In response to DCIM_Support
0 Likes
0
1313
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:28 PM . Last Modified: ‎2024-04-08 01:18 AM

Great stuff.

Thank you Bala

(CID:116360941)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:29 PM . Last Modified: ‎2024-04-08 01:18 AM

In response to DCIM_Support
0 Likes
0
1313
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:29 PM . Last Modified: ‎2024-04-08 01:18 AM

Hi Juice

Did you get your requirement met?  I.e. retain your blanking panels but have the U space report recognise these as free?  Or did you work around?  

Cheers

(CID:122688598)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:29 PM . Last Modified: ‎2024-04-08 01:17 AM

0 Likes
0
1313
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:29 PM . Last Modified: ‎2024-04-08 01:17 AM

Hello Yusuf

A new DCO U space report could be created (with StruxureWare Insight) that excludes your blanking panels

Regards

Ed

(CID:115837138)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:29 PM . Last Modified: ‎2024-04-08 01:17 AM

0 Likes
0
1313
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:29 PM . Last Modified: ‎2024-04-08 01:17 AM

Thank you ED. We unfortunately do not have this module, however, I have removed the blanking plates from DCO to get an accurate number of U-space report.

 

Many thanks

(CID:122688631)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:29 PM . Last Modified: ‎2023-10-22 01:41 AM

0 Likes
0
1313
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:29 PM . Last Modified: ‎2023-10-22 01:41 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore