DCO Server Power Modelling

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCO Server Power Modelling
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:07 PM . Last Modified: ‎2024-04-09 01:14 AM

0 Likes
3
979
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:07 PM . Last Modified: ‎2024-04-09 01:14 AM

DCO Server Power Modelling

Hi Team,

Kindly I am doing the subject configuration and wish to match up the estimated load to the measured load. Some of the Racks have metered Rack PDU that register the measured load however, the rack's summation of server nameplate values exceeds the rpdu measured load values.

Any suggestions on how to measure the actual server intake power and use it as the adjusted nameplate value without using the IT Optimize module?

Regards,

Felix

 

(CID:105462226)

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:07 PM . Last Modified: ‎2024-04-09 01:14 AM

0 Likes
1
979
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:07 PM . Last Modified: ‎2024-04-09 01:14 AM

Hi Mashwiz

It is normal that the nameplate values exceed the measured power. The nameplate value is the server vendors power rating of a fully configured server.

The most optimal way of adjusting the power rating is through IT Optimize. The reason is that the power load of the server will be adjusted according to the CPU load of the server and also the configuration of the server. Such as number of CPU's, Memory, hardidisk and etc. 

If the customer were to take a server and measure the power load of this particular server would they then be able to account for the same things as IT Optimize. They will need to make sure they test in a setup where they are sure it is running at 100% load. Do all the server have the same configuration? What happen if the customer in the future decides to add more memory or something similar to the server? 

 

But as mentioned it is normal behavior that the nameplate is above the measured load. Capacity will take the measurements into account when determine the capacity.

Based on your picture it looks like no capacity groups has been created. So your next step should be to create capacity groups.

 

Thanks

Jesper

 

(CID:105462341)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:07 PM . Last Modified: ‎2024-04-09 01:14 AM

0 Likes
1
980
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:07 PM . Last Modified: ‎2024-04-09 01:14 AM

Hi Mashwiz

It is normal that the nameplate values exceed the measured power. The nameplate value is the server vendors power rating of a fully configured server.

The most optimal way of adjusting the power rating is through IT Optimize. The reason is that the power load of the server will be adjusted according to the CPU load of the server and also the configuration of the server. Such as number of CPU's, Memory, hardidisk and etc. 

If the customer were to take a server and measure the power load of this particular server would they then be able to account for the same things as IT Optimize. They will need to make sure they test in a setup where they are sure it is running at 100% load. Do all the server have the same configuration? What happen if the customer in the future decides to add more memory or something similar to the server? 

 

But as mentioned it is normal behavior that the nameplate is above the measured load. Capacity will take the measurements into account when determine the capacity.

Based on your picture it looks like no capacity groups has been created. So your next step should be to create capacity groups.

 

Thanks

Jesper

 

(CID:105462341)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:07 PM . Last Modified: ‎2024-04-09 01:13 AM

In response to DCIM_Support
0 Likes
0
979
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:07 PM . Last Modified: ‎2024-04-09 01:13 AM

Hi Jesper, Thank you for your comment. I shall redo the capacity group as I had seen it affect the other racks. I therefore have to vehemently recommend the customer to purchase the IT Optimize license. Regards, Felix Nyakundi.

(CID:105462343)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:07 PM . Last Modified: ‎2023-10-31 10:52 PM

0 Likes
0
979
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:07 PM . Last Modified: ‎2023-10-31 10:52 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore