Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

DCO Reports

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCO Reports
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
128
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:41 PM . Last Modified: ‎2024-04-09 01:22 AM

0 Likes
15
1404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:41 PM . Last Modified: ‎2024-04-09 01:22 AM

DCO Reports

Hi All,

 

When i try to export capacity history report from AP8853 or AP8886 rack PDU on DCO Reports menu, there is an error message "no available data" (kw). Can you say any suggestion for this situation?

 

Regards 

Kerem

(CID:105461171)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 15
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:41 PM . Last Modified: ‎2024-04-09 01:22 AM

0 Likes
0
1404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:41 PM . Last Modified: ‎2024-04-09 01:22 AM

Hi Kerem, Could you please add a screen capture illustrating how your "Capacity History" report is defined - additional to the error message I'm mostly interested in seeing the selected "Equipment" and "Data type", thanks. By the way, please notice that might be a simple notification (and not error message), just simply notifying there are no available data to be reported (foe example if the selected "Date Range" dose not contain any data). Kind regards

(CID:105461291)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:41 PM . Last Modified: ‎2024-04-09 01:22 AM

0 Likes
0
1404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:41 PM . Last Modified: ‎2024-04-09 01:22 AM

Hi Jef Faridi, I attached the ss image below. I just choose capacity history in data center system room but i can't see any data as image although all rack pdu has measured value.. Regards Kerem

Capacity Report.jpg

(CID:105461315)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:41 PM . Last Modified: ‎2024-04-09 01:22 AM

0 Likes
11
1405
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:41 PM . Last Modified: ‎2024-04-09 01:22 AM

Hi Kerem,

Many thanks for sharing the screen shot - it seems you are trying to generate the report at room level, which contains no available data (displayed as a notification).  The expected report for your selected data type:

Measured failover load

Measured peak load

would have been at UPS level

 


Description of the capacity history data (including the data equipment level) is available here:
Capacity history KPI description


Kind regards

(CID:105461483)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:41 PM . Last Modified: ‎2024-04-09 01:22 AM

In response to DCIM_Support
0 Likes
0
1404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:41 PM . Last Modified: ‎2024-04-09 01:22 AM

Hi Jef Faridi, Thank you for answer. I tried that way but i can not succeeded. Although Ups has a SNMP IP and measurement values, it does not any capacity report value as you can see attached image. Regads Kerem

Capacity Report2.jpg

(CID:105461850)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:42 PM . Last Modified: ‎2024-04-09 01:22 AM

In response to DCIM_Support
0 Likes
0
1404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:42 PM . Last Modified: ‎2024-04-09 01:22 AM

Hi Kerem, Your screen shot is illustrating the report for the "Last day", I was wondering what would be the out come if you generate the report for a different Date Range, for example the last two weeks or so. By the way, if you export the report to PDF, and then open the pdf file, would you see any thing differently? However, to provide you more clear answer I would need to study your setup and server logs. If possible, please share the following files with me: 1. a copy of the latest backup file, 2. server logs (hint: http://dcimsupport.apc.com/questions/104863342/how-to-download-log-files) I will shortly send you an invite to my =S= box, just in case if you would share the files with me. Kind regards

(CID:105461856)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:42 PM . Last Modified: ‎2024-04-09 01:22 AM

In response to DCIM_Support
0 Likes
0
1404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:42 PM . Last Modified: ‎2024-04-09 01:22 AM

Hi Kerem, Many thanks for providing the files - I believe I have now the explanation for why you are not able to generate your reports. According to the server logs, your DCO have been running with incorrect date (apparently almost few weeks after its initial setup). Here is an example from yesterdays log: 2016-03-01 03:54:00.296280+02:00 [warning] 1564 Operations::OperationsMonitor::start Monitor got error while doing work: /data/monitoring/monitorStats.rrd: illegal attempt to update using time 1456797240 when last update time is 1481269819 (minimum one second step) at /usr/local/share/perl/5.10.1/Operations/PerformanceMonitor.pm line 431 2016-03-01 03:54:05.990261+02:00 [warning] 1564 Operations::OperationsMonitor::start Monitor got error while doing work: /data/monitoring/monitorStats.rrd: illegal attempt to update using time 1456797245 when last update time is 1481269819 (minimum one second step) at /usr/local/share/perl/5.10.1/Operations/PerformanceMonitor.pm line 431 The "illegal attempt to update using time..." is an indication that the measurements KPI's cannot be saved, and therefore there is no available data to be reported. Going forward, I would suggest to correct the server time & date, and if possible I would also suggest using an NTP server to synchronize the time between DCO and the external system(s) (such as DCE), more info available here: http://dcimsupport.apc.com/display/UAOp74/The+Importance+of+System+Time+Synchronization+for+Accurate... Kind regards

(CID:105461966)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:42 PM . Last Modified: ‎2024-04-09 01:22 AM

In response to DCIM_Support
0 Likes
0
1405
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:42 PM . Last Modified: ‎2024-04-09 01:22 AM

Hi jef, Thank you for your helps. I have tried an NTP server in DCO and DCE. I have successed for DCE but DCO have not success sync. As you can see the error image below, so how can I solve that.

SYNC ERR.JPG

(CID:105462538)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:42 PM . Last Modified: ‎2024-04-09 01:22 AM

In response to DCIM_Support
0 Likes
0
1405
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:42 PM . Last Modified: ‎2024-04-09 01:22 AM

Hi Kerem, You are welcome - the error message says "no server suitable for synchronization found", that's an indication of the ntp server being unreachable from your DCO. Perhaps something (like firewall) is blocking the communication between your DCO and ntp server. To verify if your ntp server is reachable, try the following command from your DCO server: ntpdate -q 'your-ntp-server' if that returns 'no server suitable for synchronization found', then it is not reachable and you might want to contact your local network administrator for advise. Kind regards

(CID:105464950)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:42 PM . Last Modified: ‎2024-04-09 01:22 AM

In response to DCIM_Support
0 Likes
0
1405
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:42 PM . Last Modified: ‎2024-04-09 01:22 AM

Thank you so much for help Mr. Jef Regards Kerem

(CID:105464996)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:42 PM . Last Modified: ‎2024-04-09 01:22 AM

In response to DCIM_Support
0 Likes
0
1405
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:42 PM . Last Modified: ‎2024-04-09 01:22 AM

You are Welcome, Kerem Kind regards

(CID:105465005)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:42 PM . Last Modified: ‎2024-04-09 01:22 AM

In response to DCIM_Support
0 Likes
0
1405
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:42 PM . Last Modified: ‎2024-04-09 01:22 AM

Hello Jef, Another NTP server is integrated successfuly, but anythings do not change for reporting i mean it is still ups report time is incorrect. If you want i can share the logs with you. By the way DCO and DCE are not sync healtly because of this reason. Many thanks Kerem

(CID:105465048)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:42 PM . Last Modified: ‎2024-04-09 01:22 AM

In response to DCIM_Support
0 Likes
0
1405
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:42 PM . Last Modified: ‎2024-04-09 01:22 AM

Hi Kerem, If the time/date is corrected on the DCO server, then the server needs some time (at least few days) to collect data and save the KPI's (otherwise there would be no available data to be reported). Kind regards

(CID:105465056)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:43 PM . Last Modified: ‎2024-04-09 01:22 AM

In response to DCIM_Support
0 Likes
0
1405
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:43 PM . Last Modified: ‎2024-04-09 01:22 AM

Hi Jef, Thank you for all helps. I synced ntp server and i will wait a few days. Webmin time is correct and DCE time is also correct so there is no differencies two software, but it is still wrong alarm value and wrong measured values. Thats actually big problem for me. Should i wait for a few days or i can send you logs. Regards Kerem

(CID:105465292)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:43 PM . Last Modified: ‎2024-04-09 01:21 AM

In response to DCIM_Support
0 Likes
0
1405
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:43 PM . Last Modified: ‎2024-04-09 01:21 AM

Hi Kerem, I'm glad to hear that your have resolved the time/date issue - that was really great because as you might have noticed the DCO server date was one month a head of the actual/real time (it was March instead of being February). If you have issues with alarms and the measurements, then you should not wait. But it is not clear to me what you mean by "wrong alarm value" and "wrong measured values" - would it be possible for you to add more description and screen captures illustrating the issue. Perhaps post it as a new question, in that way each case/question would contain well defined issue (eg. one issue per question). Kind regards

(CID:105465295)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:43 PM . Last Modified: ‎2023-10-31 10:52 PM

0 Likes
0
1405
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:43 PM . Last Modified: ‎2023-10-31 10:52 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore