Hello,
I have a question concerning DCO 8.2.2 and StruxureWare Portal 1.3.7. I have configured several portlets concerning power capacity and due to estimated load and the lack of measured data the power consumption is listed at 100%. However, I have measured PDU(s) and UPS systems.
(CID:129411258)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 03:42 PM . Last Modified: 2024-04-05 12:29 AM
Hi Brian,
You may want to use 'Predicted Power' to get DCO Power capacity to use measured power whenever available, instead of estimated load.
To achieve predicted power to be as close as measured power, set the lower & upper threshold as 1.
See here to read more on Predicted Power
(CID:129411274)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 03:42 PM . Last Modified: 2024-04-05 12:29 AM
Jef Faridi I have somewhat same concern the power capacity is calculated based on the nameplate of the equipment's
Mobily has more than 10,000 equipment's in one data center, it is impossible to get the accurate values of each equipment and that is why the power capacity gets wrong
Please i need your support in this matter that how can we get the accurate power capacity as well as cooling capacity
PS: we have sensors on ups,pdu,rectifiers and on power panels but when we connected the power path and because of the wrong nameplate KW value on equipment's the power is exceeding on ups,pdu and power panel.
There is a huge difference between the sensor value and the actual value from nameplate
Pls suggest
Thanks
(CID:129411356)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 03:42 PM . Last Modified: 2023-10-22 01:39 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.