Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

DCO 8.3.2 - Cisco UCS Manager integration is broken

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCO 8.3.2 - Cisco UCS Manager integration is broken
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
160
Jef
Jef Leader
114
gsterling
gsterling Mentor
79
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:59 AM . Last Modified: ‎2024-04-02 11:22 PM

0 Likes
4
1770
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:59 AM . Last Modified: ‎2024-04-02 11:22 PM

DCO 8.3.2 - Cisco UCS Manager integration is broken

Opened support case: #66927771

I’m running StruxureWare Operation version 8.3.2 and using Cisco UCS Manager integration in External System Configuration.

Sometime we do physical changes on Cisco UCS side:
- moving blade server from one chassis slot to another
- adding new blade servers
- replacing motherboard due to hardware failure

I think above mentioned changes are quite regular in a blade server environment.

In UCS Manager all above’s are updating correctly: I am able to see the appropriate blades’ serial number in the chassis slots after the physical changes.

But not in StruxureWare Operation! Even if the External System configuration is correct StruxureWare Operation is not showing the blades in the right physical locations.

It does not mean that none of the blade information is in DCO but after a physical movement that integration is not working as expected.

This problem generates another issue in my configuration. I also use VMware vCenter integration to follow up virtual machine information.
But for that I rely on the blade serial number information which is invalid based on above mentioned issue. Consequently the virtual machine location details from vCenter are referencing to an incorrect physical blade.

I already raised this problem a few years! ago but there was no any real solution for that. Here are some community posts:
https://community.ecostruxureit.com/questions/110005183/dco---ucs-manager-integration-is-not-updatin... [14/11/2016]
https://community.ecostruxureit.com/questions/128757950/dco---could-not-communicate-with-the-externa... [18/02/2018]
https://community.ecostruxureit.com/questions/147194440/dco---ucs-manager-list-discrepancy [11/07/2019]

Now I kindly ask the support / developers look into this issue and find a solution because the complete third party external system integration (VMware and Cisco) is useless in my environment.

Thank you in advance.

(CID:153944124)

Labels
  • Labels:
  • Data Center Operation
  • Tags:
  • bug
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:59 AM . Last Modified: ‎2024-04-02 11:22 PM

0 Likes
2
1769
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:59 AM . Last Modified: ‎2024-04-02 11:22 PM

Hi Mate,

I do recall the previously raised problems, issue seemed to be related to the external system syncing task not be executed and needed to be restarted either by rebooting or restarting the services. 

1- Do you know if rebooting the system or restarting the services "sudo systemctl restart operations" helps?

If it's okay with you, we can collect and investigate these updated data:

2- I guess this a clean 8.3.2 installation followed by restoring a backup file (from previous setup), right?

3- Which external system(s) do you now have issues with? please provide the host name and its software version details.

4- I recall you have many external sys. integrations, do you have issue with certain version(s) of those systems/Cisco UCS?

5- Can you provide a copy of the latest backup file (from DCO 8.3.2)

6- Can you provide screen captures (both from the external system and also from DCO) illustrating the issue (so we can find it in your setup).

7- Can you provide complete server log files

8- As an example. when (date and time) do you think there have been changes in real model (physical changes on Cisco UCS) that may not have been updated/reflected in DCO (this may help us to investigate the log files).

I will send you an invite to my =S= box shortly, so the data safely can be shared with me, thanks.

Kind regards 

(CID:153944586)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:59 AM . Last Modified: ‎2024-04-02 11:22 PM

In response to DCIM_Support
0 Likes
0
1769
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:59 AM . Last Modified: ‎2024-04-02 11:22 PM

Hi Jef,

1 - Yes, I applied application restarts and server reboots which are did not solve the problem. I was also let the system running after the upgrade which obviously initiated minimum an application restart but did not change anything.


2 - No, I upgraded from 8.2.12 and used internet connection option (if you remember there was another question on the community about that)


3 - I provide to you a comprehensive data in excel. I exported all UCS blade details from DCO and we have a 100% reliable database about the blades' physical location. (We also use Cisco API and pullout a report in every 24 hours.)


4 - The excel also contains the running infra firmware versions. In nutshell: we have main version 2, 3 and 4's too so we are using all the available major versions from Cisco. I'm also involved into UCS management and I can tell to you those basic API calls (serial number, blade location) what DCO is using did not change in the different versions.


5 - Sure, uploaded.


6 - Sure, uploaded. But excel spreadsheet provides more accurate information.


7 - Sure, uploaded.


8 - It is hard to remember. I try to check with more details but the forthcoming will be also good for test: we are moving 50+ servers physically so I will have day and serials number what I can provide to you.

Let me do a bit "reverse engineering" and react on the last question: Do you see from the logs when was the last update / sync between UCS Manager and DCO?

As I recall your developer was not able to see it from the log last time. In my opinion it is the key and we have to go into direction: make the DCO capable to show when was the last update received from any external system in the logs. Even better in the GUI and in case any intermittent send an email notification?

I'm open for further discussion and let me know if you need further information regarding the uploaded data.

Thanks,

Mate

(CID:153945365)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:59 AM . Last Modified: ‎2024-04-02 11:22 PM

In response to DCIM_Support
0 Likes
0
1769
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:59 AM . Last Modified: ‎2024-04-02 11:22 PM

Hi Mate,

Many thanks, it may take some time to investigate the data, but I will get back to you as soon as possible. 

Kind regards

(CID:154402914)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 01:00 AM . Last Modified: ‎2023-10-22 01:34 AM

0 Likes
0
1769
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 01:00 AM . Last Modified: ‎2023-10-22 01:34 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore