DCO 8.2.2 Client Crashes when Opening Specific Rooms

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCO 8.2.2 Client Crashes when Opening Specific Rooms
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
127
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:40 PM . Last Modified: ‎2024-04-05 02:33 AM

0 Likes
7
1254
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:40 PM . Last Modified: ‎2024-04-05 02:33 AM

DCO 8.2.2 Client Crashes when Opening Specific Rooms

Hello,

I am experiencing an issue with DCO 8.2.2. When I open a specific location and then specific room of a customer solution the thick client crashes. The room can be opened and edited fine in the web client though. I have attached an image of the DCO client error and the application log. Any assistance will be greatly appreciated because we are turning the solution over to the customer relatively soon. If you need any additional information please let me know. 

 

application.log

(CID:128762628)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:40 PM . Last Modified: ‎2024-04-05 02:33 AM

0 Likes
0
1253
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:40 PM . Last Modified: ‎2024-04-05 02:33 AM

Hi Brian,

Apparently there seem to be problem with at least one modeled item. Is it possible to ask for copy of the latest backup file - I will share a box folder with you shortly so the data can be safely shared with me, thanks.

Kind regards

(CID:128762939)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:40 PM . Last Modified: ‎2024-04-05 02:33 AM

0 Likes
0
1253
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:40 PM . Last Modified: ‎2024-04-05 02:33 AM

Jef,

I uploaded the backup to the Box Share Folder you sent. Thanks for Taking a look at this. The only thing I could see in the logs was an issue with a Rack PDU CCC-BF082-CDU2-RL2. 

 

(CID:128763223)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:41 PM . Last Modified: ‎2024-04-05 02:33 AM

0 Likes
0
1253
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:41 PM . Last Modified: ‎2024-04-05 02:33 AM

Thanks Brian,

I will get back to you asap,

Kind regards

(CID:129402740)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:41 PM . Last Modified: ‎2024-04-05 02:33 AM

0 Likes
2
1253
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:41 PM . Last Modified: ‎2024-04-05 02:33 AM

Hi Brian,

Issue seemed to be related to a rack pdu connected to a rackATS which has been moved to storage room. Simultaneously rack pdu is connected to a second rackATS in data center/room. So basically power cabling (from Storage room) is causing unexpected error.

It is now corrected and the backup file "Fixed_CCCRoomIssue_2018-03-05_13.31.tar.gz" is ready for you (in the same shared box folder).

Restoring the fixed backup file should resolve the issue.

Note: you would also need to clear the client temp files before starting the client. Client temp files are usually located in (Win) C:\Users\\.isxo\8.x (you can either rename the folder or just delete it).

Kind regards

(CID:129402848)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:41 PM . Last Modified: ‎2024-04-05 02:33 AM

In response to DCIM_Support
0 Likes
0
1253
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:41 PM . Last Modified: ‎2024-04-05 02:33 AM

Jef,

Is there anyway I can manually correct this issue or be given steps in order to resolve the issue. My customer has made changes since the last backup in their production environment. I apologize for the late reply, but I am working on multiple projects at this time.

(CID:129404637)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:41 PM . Last Modified: ‎2024-04-05 02:33 AM

In response to DCIM_Support
0 Likes
0
1253
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:41 PM . Last Modified: ‎2024-04-05 02:33 AM

Hi Brian,

I will contact you (by direct email) soon, thanks.

Kind regards

(CID:129404920)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:41 PM . Last Modified: ‎2023-10-22 01:32 AM

0 Likes
0
1253
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:41 PM . Last Modified: ‎2023-10-22 01:32 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore