Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

DCO 8.1 Colo - Unable to display measured power values

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCO 8.1 Colo - Unable to display measured power values
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 11:52 PM . Last Modified: ‎2024-04-05 04:47 AM

0 Likes
14
2410
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:52 PM . Last Modified: ‎2024-04-05 04:47 AM

DCO 8.1 Colo - Unable to display measured power values

Hi Team,

Asking on behalf of Mark Tucker our valued customer.

The issue Mark has experienced seems to be related to this post: , however we did try setting up the Design Limit and measured power is still not coming through.

Setup:

DCO version 9.1.0-70629-cf193f
DCE version 7.4.3.26
Exaple rPDUs AP8853 Application version 6.0.9

There are number of different rack PDUs monitored via DCE but for ilustration purposues we looked at a Rack with 2 x AP8853 rPDUs.

DCO rack PDUs are associated with their monitored counterparts from DCE and Rack has a 12kW Design Limit setup however no measured data is coming through:

We checked an adjusted Measurment Trending setup in DCO to "look back" for 2 days only and limited DCE settings to only last 10 days as per below:

 

However the External Systems property section on rPDUs does not display the expected power summary data and no measured readings are present in DCO Client and Web client.

One item that drew my attention was a presence of Demo External Systems:

We suspect that intial built was done using the Demo DCO built (during POC) and later copied into a full version of DCO when project started.

Not sure if this might be contributing factor to the inability of displaying the measured data.
I tried enabling the Demo Tools on Mark's DCO client (in order to remove unwanted demo external systems) but was unable do it.

Please liase directly with Mark Tucker to get this problem solved as soon as possible.

Regards
Lukasz

(CID:125211956)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 11:53 PM . Last Modified: ‎2024-04-05 04:47 AM

0 Likes
4
2412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:53 PM . Last Modified: ‎2024-04-05 04:47 AM

Hi Mark,

Server logs contain 'Read timed out' (to external system/DCE) - I was wondering perhaps your configured Timeout settings is too low for this setup. The "Stop waiting for data after", according to your screen capture, says 600 seconds - you might want to try with higher time settings (such as 3600 s) and see how it goes.

Kind regards

(CID:125213251)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 14
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 11:52 PM . Last Modified: ‎2024-04-05 04:47 AM

0 Likes
0
2412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:52 PM . Last Modified: ‎2024-04-05 04:47 AM

I would create a completely new DCO 8.1 instance, add a few racks and rack PDUs, and then connect it to the DCE server.

Then make a few device associations and verify if the problem still persists. 

This could potentially verify if (or not) the old demo solution has inherited something strange into the play ... 

(CID:125212014)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 11:52 PM . Last Modified: ‎2024-04-05 04:47 AM

0 Likes
0
2412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:52 PM . Last Modified: ‎2024-04-05 04:47 AM

Christian,

This is a customer live solution and to my knowledge he won't be able setup a new DCO to simply test it.

Also I would have expected that if this was a version 8.1 issue we would not be the first ones raising it so it must be specific to the setup, therefore I would appreciate looking further into the issue on customer production server.

(CID:125212016)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 11:52 PM . Last Modified: ‎2024-04-05 04:47 AM

0 Likes
0
2412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:52 PM . Last Modified: ‎2024-04-05 04:47 AM

Ok, it was just a suggestion on how to potentially eliminate the possibility that the demo solution is the offender.

(CID:125212028)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 11:52 PM . Last Modified: ‎2024-04-05 04:47 AM

0 Likes
0
2412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:52 PM . Last Modified: ‎2024-04-05 04:47 AM

Thank you Christian

(CID:125212036)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 11:52 PM . Last Modified: ‎2024-04-05 04:47 AM

0 Likes
0
2412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:52 PM . Last Modified: ‎2024-04-05 04:47 AM

Dear Mark Tucker and Lukasz Staciwo

We will do our best to assist you. As a start we need the server log files in order to start the trouble shooting. Would it be possible to share that with us?

You can collect server log files from the Webmin server management interface (StruxureWare DC Operation>Download server log files).

Best Regards

Anders

(CID:125212196)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 11:52 PM . Last Modified: ‎2024-04-05 04:47 AM

0 Likes
0
2412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:52 PM . Last Modified: ‎2024-04-05 04:47 AM

Server logs are available at https://schneider-electric.box.com/s/dnxoz4z60ps1p8i5u1ozk8c9t5wyw745

(CID:125212719)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 11:53 PM . Last Modified: ‎2024-04-05 04:47 AM

0 Likes
0
2412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:53 PM . Last Modified: ‎2024-04-05 04:47 AM

Hi Mark,

Can you please also share a copy of the latest backup file safely with me!  thanks.

Kind regards

(CID:125212787)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 11:53 PM . Last Modified: ‎2024-04-05 04:47 AM

0 Likes
4
2413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:53 PM . Last Modified: ‎2024-04-05 04:47 AM

Hi Mark,

Server logs contain 'Read timed out' (to external system/DCE) - I was wondering perhaps your configured Timeout settings is too low for this setup. The "Stop waiting for data after", according to your screen capture, says 600 seconds - you might want to try with higher time settings (such as 3600 s) and see how it goes.

Kind regards

(CID:125213251)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 11:53 PM . Last Modified: ‎2024-04-05 04:46 AM

In response to DCIM_Support
0 Likes
0
2412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:53 PM . Last Modified: ‎2024-04-05 04:46 AM

Hi Jef Faridi ,

    Logs attached below and settings have been changed :

 

Daily_2017-09-10_02.30.tar.gz

(CID:125213253)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 11:53 PM . Last Modified: ‎2024-04-05 04:46 AM

In response to DCIM_Support
0 Likes
0
2412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:53 PM . Last Modified: ‎2024-04-05 04:46 AM

Hi Mark,

I do not see logs attached, but I see a backup file (over two weeks old). After changing the timeout (and waiting few hours), do you see measurements appearing in DCO? If not, please collect server logs (from webmin interface) + a fresh backup file and share with me (I will send you an invite to my box folder soon), thanks.

Kind regards

(CID:125213262)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 11:53 PM . Last Modified: ‎2024-04-05 04:46 AM

In response to DCIM_Support
0 Likes
0
2412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:53 PM . Last Modified: ‎2024-04-05 04:46 AM

Hi Jef Faridi Mark Foley have shared the last  valid backup via the box link above.  Looks like the the stop waiting for data change to 3600 has worked 

 

(CID:125213338)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 11:53 PM . Last Modified: ‎2024-04-05 04:46 AM

In response to DCIM_Support
0 Likes
0
2411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:53 PM . Last Modified: ‎2024-04-05 04:46 AM

Hi Mark,

Sounds great that it is now working, many thanks for sharing the update, really appreciated. 

(just for info: I've just check my box folder, the kindly uploaded backup file is over two weeks old. It seems the issue is resolved so I will not take more of your time, but it might be good idea to check/make sure that the daily/scheduled backup is enabled/running. It is via webmin interface, StruxureWare DC Operation > Backup.) thanks

Kind regards

(CID:125213351)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 11:53 PM . Last Modified: ‎2024-04-05 04:46 AM

0 Likes
0
2411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:53 PM . Last Modified: ‎2024-04-05 04:46 AM

Hi Jef Faridi have put them up on the box. Thanks for your assitance.

https://schneider-electric.box.com/s/nwzzne0oe8go8m6kyxj3y61hdvl50whh

(CID:125213334)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 11:53 PM . Last Modified: ‎2023-10-22 01:31 AM

0 Likes
0
2411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:53 PM . Last Modified: ‎2023-10-22 01:31 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore