DCO 8.01 and APC AP 8866 Rack PDU

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCO 8.01 and APC AP 8866 Rack PDU
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:34 AM . Last Modified: ‎2024-04-08 10:45 PM

0 Likes
5
1221
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:34 AM . Last Modified: ‎2024-04-08 10:45 PM

DCO 8.01 and APC AP 8866 Rack PDU

I am trying to configure my racks and have added 2 Rack PDU's from DCE and that went fine but shouldnt I see data when I look at the operations screen?

(CID:108827134)

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:34 AM . Last Modified: ‎2024-04-08 10:45 PM

0 Likes
3
1221
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:34 AM . Last Modified: ‎2024-04-08 10:45 PM

Hi Jeffrey,

As I understand this is a fresh association/setup, and you may expect about 1 day to see the measurements in DCO. This delay time (at least 8-10 hts) for collecting data, is only for the first time device association. In general, this catch-up period ("delay time") starts when a DCE configuration is created on DCO, and it is a "gentle" catch up in order not to stress the DCE and that is why it takes so long.

And then in it should be possible to see the "Average and Peak" power values (ex. right click on rack-pdu > Properties > External Systems > Device)

Kind regards

(CID:108827154)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:34 AM . Last Modified: ‎2024-04-08 10:45 PM

0 Likes
3
1222
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:34 AM . Last Modified: ‎2024-04-08 10:45 PM

Hi Jeffrey,

As I understand this is a fresh association/setup, and you may expect about 1 day to see the measurements in DCO. This delay time (at least 8-10 hts) for collecting data, is only for the first time device association. In general, this catch-up period ("delay time") starts when a DCE configuration is created on DCO, and it is a "gentle" catch up in order not to stress the DCE and that is why it takes so long.

And then in it should be possible to see the "Average and Peak" power values (ex. right click on rack-pdu > Properties > External Systems > Device)

Kind regards

(CID:108827154)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:34 AM . Last Modified: ‎2024-04-08 10:45 PM

In response to DCIM_Support
0 Likes
0
1221
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:34 AM . Last Modified: ‎2024-04-08 10:45 PM

Are average and peak the only values I can see? Can I not highlight or drill down to get Voltage and Amperage?

(CID:108827259)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:34 AM . Last Modified: ‎2024-04-08 10:45 PM

In response to DCIM_Support
0 Likes
0
1221
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:34 AM . Last Modified: ‎2024-04-08 10:45 PM

Hi Jeffrey, You should be able to see both Watts and Amps readings, but please notice that DCO is not the monitoring unit and for the real time power readings you would need to look at your DCE. In DCO usually we can see the avg. and peak values that are based on a 30 days period (default): Configuring StruxureWare Data Center Expert integration Here is an example from my rack-pdu, just to illustrate what one might expect to see: Kind regards

Capture.JPG

(CID:108827597)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:34 AM . Last Modified: ‎2024-04-08 10:45 PM

In response to DCIM_Support
0 Likes
0
1221
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:34 AM . Last Modified: ‎2024-04-08 10:45 PM

Thanks again Jef. I am gwtting those values but I am looking for a lot more info on the DCO graphic. I obviously misunderstood what the product is. I am new to DCO but I have worked in many data centers with Schneider BMS. Those systems tend to have live data on a DCO type interface and by the looks of DCO it provides minimal information. My last question would be does Schneider provide a DIY solution similar to what I am asking. I want to monitor CRACs, UPS, PDU and Whatever else on a DCO type map with DCE type readings?

(CID:108827628)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:34 AM . Last Modified: ‎2023-10-22 01:31 AM

0 Likes
0
1221
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:34 AM . Last Modified: ‎2023-10-22 01:31 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore