DCO 8.0.1 - Cisco UCS Manager intergration best practices

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCO 8.0.1 - Cisco UCS Manager intergration best practices
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:18 AM . Last Modified: ‎2024-04-08 04:14 AM

0 Likes
10
1153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:18 AM . Last Modified: ‎2024-04-08 04:14 AM

DCO 8.0.1 - Cisco UCS Manager intergration best practices

I would like to get more information about Cisco UCS Manager intergration best practices. My questions are:

  • what type of details can be collected (e.g. blade serial, power consumption, memory, CPU, etc...)
  • how increase DCO server load this data acquisition (storage, memory requirement)
  • is there any formula which shows the number of UCS Manager and polling time interval?

The reason is why I am asking it because I would like to integrate almost 30 UCS Manager into DCO and in version 7.5 I experienced some issues.

(CID:109446963)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 10
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:18 AM . Last Modified: ‎2024-04-08 04:14 AM

0 Likes
0
1153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:18 AM . Last Modified: ‎2024-04-08 04:14 AM

I am also interested in what info you can collect. I had some issues with 7.5 data collections in the past.

(CID:109447226)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:18 AM . Last Modified: ‎2024-04-08 04:14 AM

0 Likes
1
1153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:18 AM . Last Modified: ‎2024-04-08 04:14 AM

  1. The data we query is the vendor, revision, model, serial number, number of CPUs, number of cores, total memory, available memory and average power usage.
  2. We have no numbers on how the load of DCO is affected.
  3. I don't quite understand what kind of formula you ask about. Each UCS Manager integration runs in a separate process and should not affect each other. Average power is queried at the configured interval. 

We have not tested with that amount of UCS Managers but since each integration runs in a separate process a sufficiently powerful server for DCO should be able to handle this. I am interested in what issues you experienced with 7.5. Was it the UCS Manager or DCO that had issues?

The way we query the UCS Manager have not changed between 7.5 and 8.0.1.

(CID:109447624)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:18 AM . Last Modified: ‎2024-04-08 04:14 AM

In response to DCIM_Support
0 Likes
0
1153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:18 AM . Last Modified: ‎2024-04-08 04:14 AM

Hi Kresten, Thank you for your response. Here you can find more information about my issues on 7.5: DCO 7.5 SP4 - Application status starting or non responding We are using UCS Manager version 2.2 It is possible that refresh interval was two low (15 minutes) and it generated too many data history. This is why I would like to find some kind of best practice at least about with this settting.

(CID:110004078)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:18 AM . Last Modified: ‎2024-04-08 04:14 AM

0 Likes
0
1153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:18 AM . Last Modified: ‎2024-04-08 04:14 AM

Mate Fekete - With the integration of UCS Manager do you get the chassis names, and the service profiles name auto populated? 

(CID:128747139)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:18 AM . Last Modified: ‎2024-04-08 04:14 AM

0 Likes
0
1153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:18 AM . Last Modified: ‎2024-04-08 04:14 AM

Hi Fernando,

You won't get non of these attributes with UCS integration. You will get the UCS chassis serial number and based on that you can use the batch association if you already have the S/N in DCO.

Unfortunately the service profiles are not in scope of UCS integration. I asked here in another which "API methods and functions are in use" in the integration.

Regards,

Mate

(CID:128747202)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:18 AM . Last Modified: ‎2024-04-08 04:14 AM

0 Likes
0
1153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:18 AM . Last Modified: ‎2024-04-08 04:14 AM

Mate Fekete ,

Thanks for your reply. That really sucks. It makes the UCS-M integration useless when managing multiple UCS-M's and Service Profiles/Servers move across multiple chassis. Do you know if a feature request has been made?

(CID:128747221)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:18 AM . Last Modified: ‎2024-04-08 04:13 AM

0 Likes
0
1153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:18 AM . Last Modified: ‎2024-04-08 04:13 AM

I didn't raise this request. As you can see the API methods you get couple if information from the blade. This is what I usually use and you can trace the physical location of the server if it is moving in or accross chassis.

(CID:128747283)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:18 AM . Last Modified: ‎2024-04-08 04:13 AM

0 Likes
0
1153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:18 AM . Last Modified: ‎2024-04-08 04:13 AM

So how do you get the API information such as the server to display in DCO?

(CID:128747312)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:19 AM . Last Modified: ‎2024-04-08 04:13 AM

0 Likes
0
1153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:19 AM . Last Modified: ‎2024-04-08 04:13 AM

What you can see in DCO is that what DCO collect from UCS and described in API methods. E.g.:

  • chassis serial
  • blade serial
  • blade CPU core
  • blade memory
  • chassis & blade model/type

etc... 

(CID:128748051)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:19 AM . Last Modified: ‎2023-10-22 01:29 AM

0 Likes
0
1153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:19 AM . Last Modified: ‎2023-10-22 01:29 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore