DCO 7.5 SP4 - Application status starting or non responding

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCO 7.5 SP4 - Application status starting or non responding
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:57 AM . Last Modified: ‎2024-04-08 11:11 PM

0 Likes
9
1077
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:57 AM . Last Modified: ‎2024-04-08 11:11 PM

DCO 7.5 SP4 - Application status starting or non responding

DCO 7.5 SP4 server was in hung up state after 50 days uptime. I was able to connect only via local console but I saw the following:

Reboot command did not worked as well therefore left behind only force reboot from hypervisor. After 30 mins server uptime Operation service is still not running. I already uploaded the application logs just please tell me who can work on that and I will share with him.

(CID:108825069)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 9
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:57 AM . Last Modified: ‎2024-04-08 11:11 PM

0 Likes
0
1077
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:57 AM . Last Modified: ‎2024-04-08 11:11 PM

Hi Mate, Have you checked the memory settings? it seems you setup/system has run out of memory. It says "cannot allocate memory". It would be great if you could share your server logs (and client application log) with me. Server logs can be downloaded from server webmin interface (StuxureWare DC Operation > Download Log Files > "Download log files") Kind regards

(CID:108825077)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:57 AM . Last Modified: ‎2024-04-08 11:11 PM

0 Likes
0
1077
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:57 AM . Last Modified: ‎2024-04-08 11:11 PM

Hi, I uploaded the logs and shared with you. Regards, Mate

(CID:108825138)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:57 AM . Last Modified: ‎2024-04-08 11:11 PM

0 Likes
0
1077
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:57 AM . Last Modified: ‎2024-04-08 11:11 PM

Hi Mate, Many thanks for providing the logs - will get back to you as soon as possible, Kind regards

(CID:108825142)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:57 AM . Last Modified: ‎2024-04-08 11:11 PM

0 Likes
4
1078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:57 AM . Last Modified: ‎2024-04-08 11:11 PM

Hi Mate,

According to the provided log files, there is a trace of long start up, that seems to be caused by UCS integration. During start up DCO 7.5 will fetch device data for the connected UCS managers. DCO is not completely started until data is fetched and persisted (log files indicate that it hangs on persisting the data). Scheduled jobs that perform similar tasks during operation does not seem to take several minutes.

In order to debug it might make sense to have a backup to test on.

Note: In DCO 8.0 data is not fetched during startup and should not prevent the server from starting.

Did the server start eventually?

Out of memory issue. Programs seems have used 7-8 GB more memory before server was restarted compared to right after the restart. It could indicate a memory leak. We cannot deduct what the leak is from the server log files. We could use a new set of log files in order to check if memory is currently being leaked.

Also the file (jobs.log) created by the following command could help debugging the issue:

ps -faux > jobs.log

If we can see from the new set of log files, that server is still leaking, then we might need an online session in order to debug.

Kind regards

(CID:108825408)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:57 AM . Last Modified: ‎2024-04-08 11:10 PM

In response to DCIM_Support
0 Likes
0
1078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:57 AM . Last Modified: ‎2024-04-08 11:10 PM

Hi Jef, 

Thank you for the investigation and feedback.

Yes, we have couple of UCS infrastructure which are using dedicated Managers. It would be welcome if I can use UCS Central integration instead of individual UCS Manager 😀

Did the server start eventually? No, I did not apply manual server start/reboot. It had 50 days uptime before I faced issue with the memory leakage problem. Just an additional information: DCO virtual machine can use 32GB allocated RAM and 4 vCPU.

I know about 8.0 and we already test it in our Lab and I am also planning to upgrade it in this year.

I uploaded "ps -faux" output however the file export was not worked for some reason. You can also see the latest DCO backup on appbox.

Regards,

Mate

 

(CID:108825467)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:58 AM . Last Modified: ‎2024-04-08 11:10 PM

In response to DCIM_Support
0 Likes
0
1078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:58 AM . Last Modified: ‎2024-04-08 11:10 PM

Hi Mate, You are welcome & many thanks for the info. I will get the files and get back to asap. Kind regards

(CID:108825468)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:58 AM . Last Modified: ‎2024-04-08 11:10 PM

In response to DCIM_Support
0 Likes
0
1078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:58 AM . Last Modified: ‎2024-04-08 11:10 PM

Do you have any update? Most of the users reported that facing performance issue with in DCO client which is unresponsive for 30-40 seconds and makes impossible the daily operation. I am open for a WebEx session anytime for further investigation.

I already uploaded one client log to the same store. I can see it is full with the following errors:

Error (Connection lost, response code:null) ExternalWebServiceService.getCollectedMetricDataFor() @ http://:80/isxo/core/external/ExternalWebService

(CID:108825655)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:58 AM . Last Modified: ‎2024-04-08 11:10 PM

In response to DCIM_Support
0 Likes
0
1078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:58 AM . Last Modified: ‎2024-04-08 11:10 PM

Hi Mate, Sorry for the delay, The setup contains a lot of UCS manager integration's and from thread logs it seems the server is doing a lot of (Hibernate) flushing during startup which can explain the long startup time. I had a brief discussion with our main developer, apparently the reason the start behaves differently from a normal UCS manager is because they are all done in the same go. In that way up to 10000 external items end up in the Hibernate 1st level cache, and may end with a lot of flushing. This is not an issue on DCO 8.0 since each job will do less flushing. So it is highly recommended to upgrade the product to the latest version (which contains many enhancements). Kind regards

(CID:108825662)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:58 AM . Last Modified: ‎2023-10-31 10:47 PM

0 Likes
0
1078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:58 AM . Last Modified: ‎2023-10-31 10:47 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore