Hello community.
My customer has two datacenters, in each one they have:
Before upgrade DCE 7.4.3 monitored the DCO without errors, the database status reported by DCE was normal, but now, after the upgrade of both systems (DCE and DCO + DCO-DR) the reported status:
a. The StruxureWare Operations database status is unknown
b. The Struxureware Operations Server is unreachable
In first time I think maybe a customer´s network issue could be the cause, but after check the network health and some tests I tried installing a DCE demo in version 7.5 and DCO demo in version 8.2 in my laptop using vmware player and I get the same error messages....
Community, do you have any idea about the possible reasons? Could DCO 8.2.7 be a cure for this situation? for your time and support thank you very much.
Best Regards,
(CID:132666514)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 08:21 PM . Last Modified: 2024-04-04 04:13 AM
Hi,
I had the same issue. It was solved with update of DCO to v 8.2.7
(CID:132666574)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 08:22 PM . Last Modified: 2024-04-04 04:13 AM
Dear Erlinson Bravo Garcia,
Boris Majdandzic is right, this is a very known bug that, according to Jef Faridi answer in topic :
Update:
DCO 8.2.7 is released now, contains the fix.
With respect.
(CID:132666605)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 08:22 PM . Last Modified: 2024-04-04 04:13 AM
Hello Community,
I think it´s on the dco side, I ran the isx_devicewalk and I get OID answers, when I compare with the schneiderops.xml file I can see that dce show the readed status of the respective OID example:
In dce one error alarm is: Unknown status for ETL (in red color, severity:Error)
In schneiderops.xml I think the OiD is :
-
-
-
and the result for this oid (1.3.6.1.4.1.318.1.2.2.1.5.0) in the walkfile is :
1.3.6.1.4.1.318.1.2.2.1.5.0 , Integer , 1
In the xml file the status codes for this OiD are:
-
I Think dce is reading this value and reporting the status for that, I verified the communities (public/private) all are for defect config, I don´t have firewall rules in my virtual machines ...
Any idea about this situation?
Thank you very much.
(CID:132666607)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 08:22 PM . Last Modified: 2024-04-04 04:13 AM
Ok spezialist I´m just trying to download the 8.2.7 and comment soon...
Thank you.
(CID:132666613)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 08:22 PM . Last Modified: 2024-04-04 04:13 AM
Dear Erlinson Bravo Garcia,
Tell us, please, did you solve your problem or not?
With respect.
(CID:132670092)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 08:22 PM . Last Modified: 2023-10-22 01:29 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.