Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

DCE with Easy SRV3K card APV9601 not active device alarm

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE with Easy SRV3K card APV9601 not active device alarm
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 10:31 PM . Last Modified: ‎2024-04-03 12:26 AM

0 Likes
5
1875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:31 PM . Last Modified: ‎2024-04-03 12:26 AM

DCE with Easy SRV3K card APV9601 not active device alarm

My customer have 215 Easy UPS 3KVA monitoring with DCE

 Easy SRV3K  card APV9601 not active in device alarm

How to resolve this issue?

 

 

(CID:149293385)

Labels
  • Labels:
  • Data Center Expert
  • DDF
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 10:31 PM . Last Modified: ‎2024-04-03 12:26 AM

0 Likes
3
1875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:31 PM . Last Modified: ‎2024-04-03 12:26 AM

Hi Tavorn,

 

Devices that don't use the AP9618/19 or AP9630/31/35 type of NMC 1 or NMC 2 cards do not immediately alert. if a device is in an alert state. This card would work similar ot a 3rd party card where an alert would only be seen after a poll of the device. If the device poll frequency is 5 minutes, it could take that long before DCE would see any alarms on that device.

If the device is in an alert state and you do not see an alert in DCE, I would suggest right clicking the device and requesting a device scan. Assuming the device is still in this state, when the poll occurs, DCE should then see and in turn show said alert.

If DCE does not show the alert, you would want to put the device into this state again and do an SNMPwalk of the device so that it can be compared to the DDF to verify the DDF is correctly associating the OIDs with the alarms. 

I believe the Easy-UPS devices, at least the single phase ones, use the generic UPS MIB. The larger 3 phase units use an NMC specific MIB (different than the standard APC PowerNet MIB). If you obtained a mib from this site for the unit, I'm assuming it's the latter. If you went with the standard DCE DDFs, then I'll assume it's the generic UPS MIB and associated DDF. 

If you look here:

http://www.oidview.com/mibs/0/UPS-MIB.html

It shows the generic UPS MIB OIDs. 

 

Thanks,

Steve.

(CID:149293501)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 10:31 PM . Last Modified: ‎2024-04-03 12:26 AM

0 Likes
3
1876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:31 PM . Last Modified: ‎2024-04-03 12:26 AM

Hi Tavorn,

 

Devices that don't use the AP9618/19 or AP9630/31/35 type of NMC 1 or NMC 2 cards do not immediately alert. if a device is in an alert state. This card would work similar ot a 3rd party card where an alert would only be seen after a poll of the device. If the device poll frequency is 5 minutes, it could take that long before DCE would see any alarms on that device.

If the device is in an alert state and you do not see an alert in DCE, I would suggest right clicking the device and requesting a device scan. Assuming the device is still in this state, when the poll occurs, DCE should then see and in turn show said alert.

If DCE does not show the alert, you would want to put the device into this state again and do an SNMPwalk of the device so that it can be compared to the DDF to verify the DDF is correctly associating the OIDs with the alarms. 

I believe the Easy-UPS devices, at least the single phase ones, use the generic UPS MIB. The larger 3 phase units use an NMC specific MIB (different than the standard APC PowerNet MIB). If you obtained a mib from this site for the unit, I'm assuming it's the latter. If you went with the standard DCE DDFs, then I'll assume it's the generic UPS MIB and associated DDF. 

If you look here:

http://www.oidview.com/mibs/0/UPS-MIB.html

It shows the generic UPS MIB OIDs. 

 

Thanks,

Steve.

(CID:149293501)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 10:31 PM . Last Modified: ‎2024-04-03 12:26 AM

In response to DCIM_Support
0 Likes
0
1875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:31 PM . Last Modified: ‎2024-04-03 12:26 AM

Hi Steven

Thank for prompt respond

For there EASY UPS last time I try to test by off out put and test on Battery mode there can show status on SchneiderUPS monitoring software but DCE can't show on device alarm than I wait around 1 hour never see any alarm in DCE customer ask me why different than APC smart UPS 5-8kVA

Any way... How we can improve for APC Easy UPS SRV3KI for batter than current status.

in attach I try to mib walk from UPS SRV3KI

 192.168.102.230.walk.txt

(CID:149294272)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 10:31 PM . Last Modified: ‎2024-04-03 12:26 AM

In response to DCIM_Support
0 Likes
0
1875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:31 PM . Last Modified: ‎2024-04-03 12:26 AM

Hi Tavorn,

While in this testing state, did you see the status change even though there was no alarm? For instance, if you put the UPS on battery and right click the device in DCE and request a device scan, does the state change to show it's on-battery?

If so, it may be that you have to set the thresholds for these events. I do not have one of these units to test with but I know (as I mentioned) that the single phase units use the generic UPS mib. Is this a 1ph or 3ph? I see some generic UPS oids (

1.3.6.1.2.1.33)

But I also see others that I am not familiar with. I would suggest contacting the DDF folks as it may need another DDF to get this working properly. 

Steve

(CID:149782671)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 10:31 PM . Last Modified: ‎2024-04-03 12:26 AM

In response to DCIM_Support
0 Likes
0
1875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:31 PM . Last Modified: ‎2024-04-03 12:26 AM

https://ddf.ecostruxureit.com/

(CID:149782672)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 10:31 PM . Last Modified: ‎2023-10-22 01:28 AM

0 Likes
0
1875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:31 PM . Last Modified: ‎2023-10-22 01:28 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore