Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

DCE loosing connection to XW8540 Inverters connected via Conext Combox

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase โ†’ Use quotes " " (e.g., "error 404")
  • Wildcard โ†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR โ†’ Combine keywords (e.g., login AND error, login OR signโ€‘in)
  • Keep it short โ†’ Use 2โ€“3 relevant words , not full sentences
  • Filters โ†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE loosing connection to XW8540 Inverters connected via Conext Combox
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-05 02:44 PM . Last Modified: โ€Ž2024-04-03 11:47 PM

0 Likes
13
2125
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-05 02:44 PM . Last Modified: โ€Ž2024-04-03 11:47 PM

DCE loosing connection to XW8540 Inverters connected via Conext Combox

Xantrex XW6048 inverter keeps on going offline and online in Data Center Expert causing so many Communication Lost alerts. It continuously goes online for about 5 min then goes offline for 1 minute. Readings are distorted because of this. The readings have to be in real time and available when they are needed.

 

There are 2 Conext XW 8548 E inverters connected using Xanbus through the Combox. Below is the details of the Conext Combox partnumber 865-1058.

(CID:137105978)

Labels
  • Labels:
  • Data Center Expert
  • DDF
  • Tags:
  • bug
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 13
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-05 02:44 PM . Last Modified: โ€Ž2024-04-03 11:47 PM

0 Likes
0
2125
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-05 02:44 PM . Last Modified: โ€Ž2024-04-03 11:47 PM

Dear Cleopas Chisambiro,

Regarding your problem:

Q1: Are your two inverters connected via two serial lines to the same Conext Combox?

Q2: Is the connection lost for only one of the two inverters or for both?

Q3: The lost of communication began after what events, how long (approximately)?

Q4: What version of DCE software do you have and what version of the DDF-file is used to poll two inverters through Conext Combox device?

Q5: Have you tried to find or view in any way the quality of communication over serial lines between your Conext Combox device and your two inverters? Maybe there are a lot of CRC errors, timeouts, protocol errors?

The more you provide useful information, the faster and better you will be helped here ๐Ÿ˜€.

With respect.

(CID:137106002)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-05 02:44 PM . Last Modified: โ€Ž2024-04-03 11:47 PM

0 Likes
0
2125
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-05 02:44 PM . Last Modified: โ€Ž2024-04-03 11:47 PM

Q1: Yes both are connected to the same Combox using Xanbus

Q2: It is coming from both inverters and sometimes they interchangeably loose connection

Q3:  Everything will be fine the after about 5 min the inverters looses connection for about a minute

Q4: Initially there was version 7.2.7 and we upgraded to 7.5.0 thinking the issue would be resolved. I am not sure about the DDF version, its on http://sxwhelpcenter.ecostruxureit.com/devices/view.action?deviceId=Xantrex+XW6048-230-50&vendorId=S...

Q5: If I log into the Combox while it is offline it shows all the data from the inverters including the voltages in real time.

(CID:137106065)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-05 02:45 PM . Last Modified: โ€Ž2024-04-03 11:47 PM

0 Likes
0
2125
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-05 02:45 PM . Last Modified: โ€Ž2024-04-03 11:47 PM

Dear Cleopas Chisambiro,

Q3: I wanted to know if this connection problem was from the very beginning of connecting your two inverters to DCE software, or was everything normal for a long time (month, year, etc.)? And just recently there was this connection problem?

Q4: Can you clarify the name and version of the DDF-file you use, which you downloaded from the Device Support resource and imported into the DCE software? Can you show a screenshot of the DCE software with a complete list of your Modbus DDF-files?

With respect.

(CID:137106087)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-05 02:45 PM . Last Modified: โ€Ž2024-04-03 11:47 PM

0 Likes
0
2125
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-05 02:45 PM . Last Modified: โ€Ž2024-04-03 11:47 PM

Q3: From the start it was like this. There was no change for better or for worse.

Q4: I'm not sure about the version of the DDF but the name is schneiderelectric_xantrexxw604823050

(CID:137106105)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-05 02:45 PM . Last Modified: โ€Ž2024-04-03 11:47 PM

0 Likes
0
2125
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-05 02:45 PM . Last Modified: โ€Ž2024-04-03 11:47 PM

Dear Cleopas Chisambiro,

Q3: Ok, then you should first try to increase the Modbus timeouts slightly when polling your problematic inverter devices. For example, as shown in my screenshot:

Q4: What is the version of this DDF-file? After all, you can find out this information exactly in the DCE-client.

I want to note, that it is not possible to download the DDF-file for your inverter device from the Device Support resource. It is very strange... Therefore, I asked you for exact information and necessary screenshots.

With respect.

(CID:137106132)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-05 02:45 PM . Last Modified: โ€Ž2024-04-03 11:47 PM

0 Likes
0
2125
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-05 02:45 PM . Last Modified: โ€Ž2024-04-03 11:47 PM

Q3: I have tried that one before, I set Timeout to 60sec and reties to 5, what can be the best values.

Q4: From Device Definition Files it is written version 1, you can check from the images I sent which is named "DDF files"

(CID:137106176)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-05 02:45 PM . Last Modified: โ€Ž2024-04-03 11:47 PM

0 Likes
0
2125
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-05 02:45 PM . Last Modified: โ€Ž2024-04-03 11:47 PM

Dear Cleopas Chisambiro,

Q3: In this case, you should definitely check the serial line comm settings on your Conext Combox. It is also necessary to see, if possible, the quality of data transmission over a serial line. The problem may not be in DCE software, but in the correctness of the serial comm settings of your Conext Combox.

Q4: But I do not see you showing any images...

With respect.

(CID:137106186)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-05 02:45 PM . Last Modified: โ€Ž2024-04-03 11:47 PM

0 Likes
0
2125
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-05 02:45 PM . Last Modified: โ€Ž2024-04-03 11:47 PM

Q3: It uses an RJ45 port and an ordinary cat6a cable with a terminating resistor at the end. Everything looks fine in the Combox because it has a GUI with real-time value. I will check if there are ways to check errors in the serial communication.

Q4:

(CID:137106229)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-05 02:45 PM . Last Modified: โ€Ž2024-04-03 11:47 PM

0 Likes
0
2125
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-05 02:45 PM . Last Modified: โ€Ž2024-04-03 11:47 PM

Dear Cleopas Chisambiro,

Ok, thanks for the screenshot. I will wait for further information about the serial lines comm settings of your devices.

With respect.

(CID:137106367)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-05 02:45 PM . Last Modified: โ€Ž2024-04-03 11:47 PM

0 Likes
0
2123
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-05 02:45 PM . Last Modified: โ€Ž2024-04-03 11:47 PM

Dear Cleopas Chisambiro,

Tell us please, did you solve this problem or not?

With respect.

(CID:137109215)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-05 02:45 PM . Last Modified: โ€Ž2024-04-03 11:47 PM

0 Likes
0
2123
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-05 02:45 PM . Last Modified: โ€Ž2024-04-03 11:47 PM

Not yet. The products on are the customer's site and we are still yet to agree on the time to look into it.

(CID:137110207)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-05 02:46 PM . Last Modified: โ€Ž2024-04-03 11:47 PM

0 Likes
0
2123
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-05 02:46 PM . Last Modified: โ€Ž2024-04-03 11:47 PM

Dear Cleopas Chisambiro,

I have already received the above Modbus DDF-file and I will wait for news from you on this issue.

With respect.

(CID:137110228)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-05 02:46 PM . Last Modified: โ€Ž2023-10-22 01:25 AM

0 Likes
0
2123
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-05 02:46 PM . Last Modified: โ€Ž2023-10-22 01:25 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

Youโ€™ve reached the end of your document

WHATโ€™S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore